Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

zero sequence Current Transformer

Status
Not open for further replies.

azamfaez77

Electrical
Jul 26, 2011
14
what is the purpose to use zero sequence current transformer? In what application that we need to use this?
 
Replies continue below

Recommended for you

Cable feeders in an industrial plant. Zero sequence CT around all three phase conductors only sees fault current, not load current. The ground fault relay can be set very sensitive.
 
rcwilson, is a zero sequence current transformer same as core balancing CT? Because a core balancing CT is also used to detect only fault condition. (Present around 3 phase Conductors)
 
A Core balancing current transformer and a zero sequence current transformer are the same thing.
 
Status
Not open for further replies.

Part and Inventory Search