Zero Sequence Imp (ZSI) of Transmission Line 2

Status
Not open for further replies.

HiSet

Electrical
Oct 10, 2002
70
Test setup for measuring zero sequence impedance of a line is to short all three phases and then measure the loop impedance between shorted conductors and earth return.Question I have is that ,do we we need to multiply measured ohmic value by three to get actual zero sequence impedance?
 
Replies continue below

Recommended for you

That is correct. The measurement gives Zo/3, so you multiply the value by 3 to get the actual Zo value of the line.
 