- 132
Dear All,
If the cable has neutral conductor, is the zero sequence impedance calculated different?.I have difficulty figuring out how the consultant has come up with the Z(on) at the end.
PRIMARY SUPPLY SYSTEM
Z0 0.586 < 82.88 100 MVA
0.0726 +j 0.5812 100 MVA
SUPPLY TRANSFORMER
Primary Voltage 44 KV
Secondary Voltage .6 KV
ONAN Rating 2.5 MVA
Ratio X/R 9.846 [typical]
Impedance 5.65% on base
Include tolerance -7.50% [MIN]
5.226% < 84.20
Zmin=0.528%+j5.200%
0.2112+j2.080
600 V CABLES
750 MCM Cu
14.9352 m RUN LENGTH
49 ft RUN LENGTH
6 CONDUCTOR/PHASE
6 NEUTRAL CONDUCTOR
Z 0= 0.05689 +j 0.60363 ? per mi
= 0.00053 +j 0.00560 ? actual
= 0.14665 +j 1.55607 ? on
= 1.56297 < 84.62 ? p.u.
Z(on)=.38990+j3.89204
Max Line to ground =33200A
If the cable has neutral conductor, is the zero sequence impedance calculated different?.I have difficulty figuring out how the consultant has come up with the Z(on) at the end.
PRIMARY SUPPLY SYSTEM
Z0 0.586 < 82.88 100 MVA
0.0726 +j 0.5812 100 MVA
SUPPLY TRANSFORMER
Primary Voltage 44 KV
Secondary Voltage .6 KV
ONAN Rating 2.5 MVA
Ratio X/R 9.846 [typical]
Impedance 5.65% on base
Include tolerance -7.50% [MIN]
5.226% < 84.20
Zmin=0.528%+j5.200%
0.2112+j2.080
600 V CABLES
750 MCM Cu
14.9352 m RUN LENGTH
49 ft RUN LENGTH
6 CONDUCTOR/PHASE
6 NEUTRAL CONDUCTOR
Z 0= 0.05689 +j 0.60363 ? per mi
= 0.00053 +j 0.00560 ? actual
= 0.14665 +j 1.55607 ? on
= 1.56297 < 84.62 ? p.u.
Z(on)=.38990+j3.89204
Max Line to ground =33200A