Gonenc
Electrical
- Jun 18, 2020
- 7
Hi;
I am trying to enter related information to zigzag grounding transformer on ETAP. Our transformer information are below. BUT, when I enter 18,2 ohm/phase to Impedance OHM subtitles, phase to ground current is limit to much. As much as I read, zero sequence of zigzag transformer should be very low. Please see below screenshot and please tell me what should I enter these gaps. OR these required ohm and X/R information base on zero sequence ?
System Voltage (L-L)=10,5Kv
Irated/phase=100A
Short Circuit current in neutral=1000A, 10sec
Ohm/per phase = 18,2 ohm/phase
I am trying to enter related information to zigzag grounding transformer on ETAP. Our transformer information are below. BUT, when I enter 18,2 ohm/phase to Impedance OHM subtitles, phase to ground current is limit to much. As much as I read, zero sequence of zigzag transformer should be very low. Please see below screenshot and please tell me what should I enter these gaps. OR these required ohm and X/R information base on zero sequence ?
System Voltage (L-L)=10,5Kv
Irated/phase=100A
Short Circuit current in neutral=1000A, 10sec
Ohm/per phase = 18,2 ohm/phase