Aspiring mechanical engineer here looking for some advice with some zonal airflow questions. I am in CA for code reference;

I am working on designing a 3-zone system using a single-speed AHU. This is a residential home with uneven zone area. I.e. 3 floors with say 700 Sq Ft Top floor, 1500 Sq Ft Middle Floor, and 700 Sq Ft bottom floor. I calculated my Airflow using the equation in Manual J as follows;

Total required airflow for cooling: (Sensible Capacitiy) / 1.1 * TD = CFM
Total Sensible capacity: 27,878 BTU
I am using the assumption of a low latent load and based on manual J tables a TD of 17 is required;

(27,878) / (17)*(1.1) = 1490.80 --> Selecting the next nominal tonnage up I would select a 1,600 Nominal CFM unit.

Now for my predicament;

When in single-zone operation I have a ton of additional airflow on the top floor operation and bottom floor operation. Does anyone have experience dealing with mitigation of this airflow?

I have used bypass but have concerns that using too large of a bypass will cause my coil to freeze. I am also under the impression that new 2013 California Energy Code will make using a bypass difficult if not impossible. I have thought of dumping air into the attic or outside but was told this is counter-intuitive to energy efficiency.

Should I be worried about getting proper air entrainment at my bottom floor? What is an acceptable limit on bypassed airflow? What should I do if bypasses are prohibited in the new code?

Thank you all in advance. I look forward to learning a lot in here!

Best Regards,

Brad
 
Replies continue below

Recommended for you

You could perhaps downsize and try to count on usage diversity.

But really your approach is unlikely to ever satisfy owner expectations.

You need variable flow.
 
Thanks MintJulep! Definitely made that consideration and I agree it is truly the best solution for this situation. Just getting the buy in on that extra $$ has been the biggest hurdle. Do you have any thoughts on dumping extra air to a low-impact area such as a stairwell or to the alternate zones? A large concern with this method has been how the impact changes in heating vs cooling application.
 
I don't think any hammer-and-tongs solutions are a good idea. Bite the bullet and use variable air volume.
 