FIRE DAMPER LOCATIONS 2

Status
Not open for further replies.

24121965

Mechanical
Aug 25, 2005
3
NG
What are the criterias that that to be considered to identify locations for installing fire dampers in HVAC system.
 
Replies continue below

Recommended for you

Where your ducts and openings pass through a fire separation as determined by the architect a fire damper is required.

In some instances you can run your duct within a fire-rated enclosure passing through a rated room and avoid the fire damper. The enclosure effectively creates a space outside of the rated room.
 
IMC has 2 definitions ..... fire barriers and fire partitions ........ also sprinklered and non-sprinklered

I spec UL-555 dynamic rated dampers with the curtain out of the airstream
 
There is an example drawing in NFPA 90A that gives many common duct and damper possibilities. Good info in a small (one page) package!
 