We have in our NGL Plant, 3 explosion - proof small motors rated 1.5 HP,230 VAC, 3 Phase.Those motors have experienced repeative failures which led to 2 motors burnt out to-date.
Further, our investigation revealed that the motor failure occurred during mechanical seizure in the pump unit, which caused a locked-rotor condition. It failed due to exposure to a prolonged or sustained overload, since the the control circuit is only protected by a 15 Ampere Circuit Breaker, with no additional motor protection.The high load current experienced at this condition, possibly reaching as high as 34 Amperes based on the motor design, which caused deterioration of the winding insulation and eventual motor burnt out because of overheating.
Is it possible to review the existing control circuit and provide an additional motor protection against prolonged overload condition?
Further, our investigation revealed that the motor failure occurred during mechanical seizure in the pump unit, which caused a locked-rotor condition. It failed due to exposure to a prolonged or sustained overload, since the the control circuit is only protected by a 15 Ampere Circuit Breaker, with no additional motor protection.The high load current experienced at this condition, possibly reaching as high as 34 Amperes based on the motor design, which caused deterioration of the winding insulation and eventual motor burnt out because of overheating.
Is it possible to review the existing control circuit and provide an additional motor protection against prolonged overload condition?