Yesterday I trip tested a newly installed dry pipe system having a capacity of 1,409 gallons using city water only (no fire pump) with results as follows:
Static Pressure 61 psi
Residual Pressure 58 psi
Pitot Pressure: 35 psi (2 1/2" Hydrant Butt)
Rate of Flow 993 gpm
Flat roofed building with sprinklers 25' above the static/residual fire hydrant.
I've successfully trip tested some 1,250 gallon capacity systems but they always had a large fire pump with with a lot of kick behind it. Never something this big. What I had was a 6" valve on 6" riser manifold fed from 10" city water main through 100' of 6" underground which included a 6" meter and 6" Ames 2000ss double check.
System had a capacity of 1,409 gallons (yeah, it was really that big) having 100' of 6" feed main with two 4" mains and 2" branch lines on tree system.
I wasn't completely nuts because when we laid out the system I did it in such a way we could have easily manifolded the riser making two systems of less than 750 gallons involving a days extra labor and the cost of a dry valve with trim. When I laid the system out I did so anticipating failure. I even went so far as to warn the AHJ that I was experimenting, the reasons why I was experimenting and being the understanding sort he was as curious as I was to see if it would work. If I did fail at least I wouldn't have all kinds of egg on my face.
When I bid the job I had the price for a manifold riser so it wasn't like the additional cost of failure would be overly high.
Here is what I got.
Time to trip was nearly instant and I think I got maybe 1 1/2 seconds. Total time to water to reach the inspectors test (1/2" SBO) was 0 minutes and 58 seconds.
Here is what helped me and might someday help some of you.
A few months ago I got bored and for some easy late night reading I spent a few hours going over paper by James Golinveaux, Sr. Vice President, Research & Development Tyco Fire & Building Products
For my fellow technicians out there this is very much a worthwhile read!
A Technical Analysis: Variables That Affect The Performance Of Dry Pipe Systems
If you haven't seen it it's good stuff throughout but especially starting on page 14.
For the dry valve I used the Reliable 6" DDX-LP Dry Pipe Valve System with accelerator which required only 15 psi of air.
Trip time was nearly instant, less than two seconds on my stop watch, with a steady stream of water delivered to the inspectors test in 0 minutes and 58 seconds. All this through a half inch orifice to boot!
Word of advice, on a system this big I would always leave myself some sort of easy out in the event of failure.
If you do the kind of work I do read that analysis because it is well worth your time... to help I also did a little trick with a 1" "loop" on the last two branch lines to allow air to compress in the closer non flowing main instead of being forced out of the inspectors test. I think it worked.
Best part of all this? The fitters were all betting me beer it wouldn't work and I won. You should have seen their faces.
Static Pressure 61 psi
Residual Pressure 58 psi
Pitot Pressure: 35 psi (2 1/2" Hydrant Butt)
Rate of Flow 993 gpm
Flat roofed building with sprinklers 25' above the static/residual fire hydrant.
I've successfully trip tested some 1,250 gallon capacity systems but they always had a large fire pump with with a lot of kick behind it. Never something this big. What I had was a 6" valve on 6" riser manifold fed from 10" city water main through 100' of 6" underground which included a 6" meter and 6" Ames 2000ss double check.
System had a capacity of 1,409 gallons (yeah, it was really that big) having 100' of 6" feed main with two 4" mains and 2" branch lines on tree system.
I wasn't completely nuts because when we laid out the system I did it in such a way we could have easily manifolded the riser making two systems of less than 750 gallons involving a days extra labor and the cost of a dry valve with trim. When I laid the system out I did so anticipating failure. I even went so far as to warn the AHJ that I was experimenting, the reasons why I was experimenting and being the understanding sort he was as curious as I was to see if it would work. If I did fail at least I wouldn't have all kinds of egg on my face.
When I bid the job I had the price for a manifold riser so it wasn't like the additional cost of failure would be overly high.
Here is what I got.
Time to trip was nearly instant and I think I got maybe 1 1/2 seconds. Total time to water to reach the inspectors test (1/2" SBO) was 0 minutes and 58 seconds.
Here is what helped me and might someday help some of you.
A few months ago I got bored and for some easy late night reading I spent a few hours going over paper by James Golinveaux, Sr. Vice President, Research & Development Tyco Fire & Building Products
For my fellow technicians out there this is very much a worthwhile read!
A Technical Analysis: Variables That Affect The Performance Of Dry Pipe Systems
If you haven't seen it it's good stuff throughout but especially starting on page 14.
For the dry valve I used the Reliable 6" DDX-LP Dry Pipe Valve System with accelerator which required only 15 psi of air.
Trip time was nearly instant, less than two seconds on my stop watch, with a steady stream of water delivered to the inspectors test in 0 minutes and 58 seconds. All this through a half inch orifice to boot!
Word of advice, on a system this big I would always leave myself some sort of easy out in the event of failure.
If you do the kind of work I do read that analysis because it is well worth your time... to help I also did a little trick with a 1" "loop" on the last two branch lines to allow air to compress in the closer non flowing main instead of being forced out of the inspectors test. I think it worked.
Best part of all this? The fitters were all betting me beer it wouldn't work and I won. You should have seen their faces.