Please help me,

Is there anybody who knows which code explains about minimum Radius on a curvature tendon? Is there any formula/calculation method for this minimum radius? And if the Prestressed Tendon Curvature follows the minimum radius, does that mean Hairpin Reinforcements become unnecessary? Thank you.
 
Replies continue below

Recommended for you

2.5m is a generally accepted minimum radius for bonded PT 19mm ducts.

 
Section E of this PTI document deals with this issue and agrees with Trenno: PTI Tech Note.

Lean_1_oonmng.jpg

Lean_2_icnjjc.jpg


I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
 
Normally this information is supplied by the prestressing company.

A basic rule for multi-strand tendons is 70 * duct diameter. This obviously assumes a logical duct diameter for the number of strands as the bearing stresses are related to the number of strands and the bearing area! It is not a good idea to use less than this.

Your question about hairpins is far too general to answer. I would not think that hairpins would overcome the concrete crushing and bursting problems that you get from too tight curvature. Or the duct wear or higher friction. So I would assume that they are there for another reason.
 
Thank you everyone. This really helps me.

@rapt: What do you mean? Isn't the hairpin used to bear the lateral force due to the curvature? For bursting, I think we use Bursting Reinforcement.
 
I doubt that the hairpin would develop much stress before the concrete was in trouble due to high compression stress. It may stop a failure but it will not reduce the compression stress significantly in my opinion.

Hairpins might work to stop breakout/spalling where an angle change is near a surface and towards the surface as happens at kinks in tendons near anchorages in large bridges etc. In a general area where it is concrete crushing that is the problem, I doubt that they would alleviate the problem as the concrete would have to crush before they were fully activated.
 