AS1170.4 Section 7 Vertical earthquake actions 1

Status
Not open for further replies.

rscassar

Structural
Jul 29, 2010
631
How do people account for the vertical earthquake actions required as part of section 7. My previous approach (using Etabs), was to select mass as a vertical and lateral mass, increase the modes to account for all the slab bouncing modes, and apply the accelerations as U3 (Uz) = 0.5*9.81.

As this creates so many modes from floors bouncing up and down, I'm thinking of removing the vertical mass, just considering the lateral mass and lateral modes, and then applying the vertical earthquake actions as 0.5*kp*Z*Ch(Tv)*Sp (0.5*1.0*0.08*3.68*0.77 = 0.12). And add this in the combinations, so creating 4 further cases in addition to 1.0DL+0.3LL+/-EQ being 1.15DL+0.35LL+/-EQ and 0.85+0.25LL+/-EQ .
 
Replies continue below

Recommended for you

In NZ it's intended to be an additional force, additive to other combinations as deemed necessary. An equivalent static vertical action if you like. Suspect the same intent applies for Australian code as you've outlined.

I've never heard or seen of anyone trying to do a vertical modal analysis to apply vertical design actions, it strikes me as being fundamentally incorrect. The derivation/prediction of vertical loading isn't so well understood as the lateral components. Simplification such as vertical period is equal to zero are good enough given all of the other assumptions being made.

In NZ at least, vertical actions very rarely governs over a 1.2G & 1.5Q ULS case since the load case you'd add to would be 1.0G & 0.3Q & E. So the vertical earthquake multiplier would need to be quite significant for it to govern for a strength requirement (basically would need E to be more than 0.2G + 1.2Q to be higher than 1.2G + 1.5Q). SLS governing is a possibility depending on how sensitive your structure is to vertical excitations, but then the seismic actions at SLS are a quarter of the ULS actions in NZ.



 