Is ACI 318-14 Section 25.4.10 development length reduction applicable to pedestal anchorage?

Status
Not open for further replies.

MJC6125

Structural
Apr 9, 2017
120
I'm wondering if section 25.4.10 of ACI 318-14 is applicable for reducing the development (lap) length required in a pedestal anchorage situation where you are attempting to lap steel column base plate anchors with vertical reinforcement in a concrete pedestal. This reduction is the one where you reduce the required development length by the ratio As,required/As,provided.

I have used the Windianto paper called Design of Anchor Reinforcement in Concrete Pedestals for these situations in the past. And in that paper they use the development length reduction per the image below.

Capture_pmot0g.png


However, I'm seeing in ACI 318-14 section 25.5.1.4 that this reduction is not allowed in lap splice situations. I know the pedestal anchorage situation is different than a traditional lap splice, but I'm not 100% sure if it's different enough to where I can consider development length only and neglect the section 25.5 lap splice requirements. Does anyone have any guidance on whether the Ld development length reduction is allowable in the pedestal anchorage situation? If so, why is it acceptable here, but if we were dealing with reinforcement lapping it would not be?
 
Replies continue below

Recommended for you

[quote.... However, I'm seeing in ACI 318-14 section 25.5.1.4 that this reduction is not allowed in lap splice situations.][/quote]

You did not mention if it is for Seismic Design Categories C, D, and E..

You may reduce the development length when excess reinforcement is provided per ACI 318 ..except ;

Copy and paste of the relevant clause 25.4.10.2, ACI 318-14

(a) At noncontinuous supports
(b) At locations where anchorage or development for fy is
required
(c) Where bars are required to be continuous
(d) For headed and mechanically anchored deformed
reinforcement
(e) In seismic-force-resisting systems in structures
assigned to Seismic Design Categories D, E, or F








Tim was so learned that he could name a
horse in nine languages: so ignorant that he bought a cow to ride on.
(BENJAMIN FRANKLIN )

 
Ah yes, I guess this question is specific to Seismic Design Categories A-C.

It sounds like you are saying the reduced development length rule is applicable to this scenario. Do you know why it is acceptable to use the reduced development length in this condition, but it would not be acceptable to use it in a normal lap splice condition? See two cases below for reference. I'm wondering what the difference is between those two scenarios where one allows it and one does not.