I have a small 1-story control building for a wastewater treatment plant that houses blowers and other mechanical equipment.
The 8" thick hollowcore roof of this structure supports a crane rail and a rolling 2-ton hoist. My employer has used this setup for many years, but I have never felt comfortable about the hoist setup; and have been able to avoid sealing the sheets for the 6 years I have been here. One of the older engineers in the office always sealed the sheet.
The older engineer is gone now and I'm stuck with the hoist detail on two current projects. See below:
There are no posts supporting the crane rail. The system relies upon composite action and sharing of load between pre-cast panels.
Questions:
Overall, question....What can I do to improve this setup?
[ul]
[li]I think that If I have a 2 ton hoist, then the normal OSHA/ASME rules would apply and the hoist's supporting structure needs to have a safety factor of 5? (Design point load of 20kips) (edited)[/li]
[li]The pre-cast panels are a delegated design item. I could specify that the panels be designed for the 2-ton hoist and have it be part of the pre-casters' sealed submittal? I'm not confident at all that these hollow core panels can handle a 20kip point load though. (specifically the shear load)[/li]
[li]I could design a cast-in-place roof that I do have confidence works for the hoist; and then allow the contractor to submit sealed sheets for alternative designs if they have a better idea?[/li]
[/ul]
What do you think?
The 8" thick hollowcore roof of this structure supports a crane rail and a rolling 2-ton hoist. My employer has used this setup for many years, but I have never felt comfortable about the hoist setup; and have been able to avoid sealing the sheets for the 6 years I have been here. One of the older engineers in the office always sealed the sheet.
The older engineer is gone now and I'm stuck with the hoist detail on two current projects. See below:


There are no posts supporting the crane rail. The system relies upon composite action and sharing of load between pre-cast panels.
Questions:
Overall, question....What can I do to improve this setup?
[ul]
[li]
[li]The pre-cast panels are a delegated design item. I could specify that the panels be designed for the 2-ton hoist and have it be part of the pre-casters' sealed submittal? I'm not confident at all that these hollow core panels can handle a 20kip point load though. (specifically the shear load)[/li]
[li]I could design a cast-in-place roof that I do have confidence works for the hoist; and then allow the contractor to submit sealed sheets for alternative designs if they have a better idea?[/li]
[/ul]
What do you think?