SRE--thank you for getting real with me. I've always appreciated your critique. I'll try my best to give a full account below. Apologies for the long-windedness, but I'm trying to be as thorough and transparent as possible. See attached too. I don't disagree that this is getting into means and methods; but I am trying to help rectify an unexpected situation, and I'm not sure who else to turn to.
Some background on this project: this is the floor of an existing conveyor gallery. Roughly 11'-6" x 42'-0", sloped. Surrounding this gallery is a crushed rock stockpile that has just gone through crushing and transported by other conveyors. It is impossible to work safely near/below this gallery unless crushing operations are shutdown and rock isn't being dumped onto the pile. It is also impossible to work safely inside the conveyor gallery/on the gallery floor (this project) unless that conveyor is also shutdown. Both the crusher operation and this particular conveyor have been shutdown this week (10/9-10/13). That is the window of opportunity I have to work with. Contractor is working 24 hr days.
1. Conveyor gallery was constructed in 1970s. Floor is hosed frequently for material buildup and freezes in the winter. De-icing salts are used (and have been used for years before I was hired).
2. May 2023 - a 3 ft diameter of concrete slab broke free and fell 20 ft below. Now there is a big hole in the slab. We closed off access to the gallery.
3. Over the next few weeks, I designed a replacement slab, appealed to management the need for additional, unplanned infrastructure budget, and began construction bidding. I kept the replacement slab similar to original design but went through the appropriate calcs.
4. For metal form deck, I originally required non-composite 1.5C-36 (18 gage) Gr. 50, assuming two-span condition. (I looked through the same Vulcraft tables you included above and also used Vulcraft's unshored construction span deck design aid.) Looking back through my notes, I used DL=66 psf (accounting for avg thickness with 1.5" deck) and construction LL=20 psf. I forgot about the smaller value in my more recent calcs. I tried to be a bit conservative since I haven't encountered an overhanging deck condition before.
5. Contractor was selected, and contractor ordered materials. Neither of us worked with a separate party to complete a detailed design of the form deck. I assumed contractor would order what I called out, and I assumed form deck sheets would come in 14+ ft lengths.
6. September - A few weeks before the one-week construction window was scheduled, contractor informed me that the 18 ga. deck was taking very long to procure and was concerned about it arriving in time. However, 20 ga. deck was available immediately. I double checked my calcs/notes from May and checked Vulcraft and saw that 20 ga. appears to be ok for 7 ft span in a 2-span condition. I informed contractor that I would still prefer 18 ga. but the 20 ga. would be ok in a pinch.
7. October (this week) - Mob and demo began Monday, 10/9. Contractor is working 24 hr days. I check on them once or twice a day. Contractor found some additional structural steel corrosion that we repaired.
8. Tuesday, 10/10 at around 6 pm - I learned that the form deck is only 13 ft long. Contractor said they plan to arrange it to try to keep the overhanging sections as short as possible. I didn't provide any feedback/recommendations at that time. I first called a former colleague with 15+ years experience. He hadn't personally dealt with a situation like that but gave me some advice on what steps I could follow. He suggested calculating the actual required moment vs. available moment using section modulus values from Vulcraft tables.
9. Same Tuesday evening - I did some reading from literature before diving into calcs (SDI Manual of Construction with Steel Deck 2nd Ed; SDI NC-2017). The SDI Manual of Construction has one example on pg. 38 (see attachment) on penetrations that is somewhat similar to my case. They're just checking fb = M/S.
10. Using the section properties for the 20 ga. deck (unsure of what actually came on site), I went through the calcs that I attached in my earlier reply. I used DL = 75 psf and LL = 40 psf, which I believe may both be a bit conservative.
11. Tuesday around 9 pm - I sketched a rough arrangement of what I believed would be the best overlap condition for the 13 ft long deck sections. I walked over to the contractor's overnight crew and provided sketch to discuss. We talked through potential issues. One of their more experienced iron workers mentioned having recently worked on a bridge that had some mid-air lap splices. For that, they worked with an approved and inspected detail that had several deck screws installed at the lap.
12. Without me bringing up any further ideas/requirements, contractor proposed installing deck screws at every rib at these mid-air lap splices. Also proposed taking an angle (L4x4x3/8 or similar) and installing below the exposed edge of each lap. Angle would be oriented perpendicular to deck span and welded to truss bottom chords. No, an angle is obviously not the greatest flexural member, but it's what we had on site to work with. While not being able to take much serious load, I believe the angle would still help with limiting deck deflection at that mid-air lap. I thought their proposed ideas would be helpful.
Side note--the following morning, I checked on the deck gage with my main contact for the contractor, and he said the 18 gage actually did arrive in time. I asked for the receipt/slip on the decking, which I should be receiving soon.
This reply is already too long, but I'll gladly answer other questions. SRE, you are correct about 75 psf DL + 40 psf LL exceeding the allowable for 20 gage deck in Vulcraft's span tables. Like I mentioned above, I originally selected the deck size (18 gage) in May based on 65 psf DL (5.25 avg slab thickness) + 20 psf construction LL, but in my haste this Tuesday evening, I had forgotten that and used 40 psf LL instead. The calculations I did on Tuesday took into account actual vs. allowable bending stresses (f = M/S). I did not consider the Vulcraft span tables because I figured they were no longer applicable given my unique situation. I've been working 12-14 hours days this week to try to stay on top of issues as they come up and keep the workers safe. I have no interest in cutting corners or doing something unsafe. The parties involved on this project are myself (owner and designer), the contractor, and a certified inspection firm. Who else should I turn to? I haven't reached out directly to Vulcraft, but perhaps I should.
SRE, What other glaring issues do you see? I ask this sincerely; hopefully none of this has come across as an excuse or attempt to dodge accountability. I'm genuinely interesting in learning about what other issues you see, considering my fb = M/S values appear to be below allowable stress given 20 psf construction LL. What have I done wrong? I'm only 5 years out of college, so I obviously have not turned over every rock in structural engineering.