Good afternoon,

I come across this situation all the time and I wanted to see if anyone here had a response to how they handle it. Very often I come across HVAC equipment that lists FLA/RLA, MCA and MOCP, where the MOCP listed is actually <125% FLA.

Now I know MOCP is often referred to as being calculated as (225% largest load + 100% remaining loads) and then round DOWN to the next standard size. What I don't understand is how this is really a "complete framework" of thinking, so to speak. One consideration for example is that most overcurrent protection is 80% rated such that if this HVAC package is a continuous load, I can't select overcurrent protection where the FLA > 80% OCPD. Yet often this will end up in conflict with the vendor's listed MOCP which is often smaller than 125% FLA.

Any thoughts from anyone? Have a great day.
 
Replies continue below

Recommended for you

If you are under the NEC, you use whatever is listed by the manufacturer for MCA and MCOP. Pretty simple. The rest is not relevant. If you are using 125% of the largest motor, you don't need to limit the breaker loading to 80%. 80% is the inverse of 125%. If you size everything per the NEC, the 80% continuous loading for breaker is accounted for by the 125% factor already applied.

Also it's possible that not all motors or loads in an HVAC package run simultaneously. If you use breakers larger than the MCOP, that's an NEC violation.
 