Calculated neutral current not matching measured neutral current 4

Status
Not open for further replies.

edison123

Electrical
Oct 23, 2002
4,451
3 Ph, 415 V, 50 Hz 4 wire, neutral solidly earthed system feeding a high school with 3 phase ac's, LED & fluorescent lamps, ceiling fans, UPS systems for computers, lab equipments etc.

Current and voltage THD's in each phase <3%.

Current harmonics 3rd to 13th less than 0.5% in all 3 phases as per below photo

RY – 400 V YB – 401 V BR – 402 V

R – 135 A Y – 188 A B – 167 A

Using the formula, neutral current = Sqrt [(R^2 + Y^2 + B^2 – RY – YB – BR)], I get 46 A. (Online calculators also give 46 A neutral current).

But the measured neutral current is only 18 Amps.

Would appreciate any explanations.

03_-_Harmonics_-_Current_B_egbq3q.jpg




Muthu
 
Replies continue below

Recommended for you

Neutral current should be = Vector sum of currents in all three phases. So, you need phasor angless.
 
Those numbers may make sense on a "High Leg" delta system, maybe not but have to ask. eg:


--------------------
Ohm's law
Not just a good idea;
It's the LAW!
 
My experience with unexpected neutral currents was with a single phase system when the neutral was unexpectedly high.
That was a power factor issue.
One line to neutral load was at a very low power factor,the other at a much better power factor.
On single phase, it is easy to see that any power factor, or phase angle difference, will increase the current, not decrease it.
But shushilksk's post kicked my mind into gear.
It may not be safe to assume that the entire current difference is phase to neutral current.
I suspect that you have unbalanced line to line loads that are not affecting the neutral current.
And you may have unbalanced line to line power factors which will drive up the line to line unbalance but not affect the neutral current.
(Thanks for the mind jog, shushilksk)

--------------------
Ohm's law
Not just a good idea;
It's the LAW!
 
"..RY – 400 V YB – 401 V BR – 402 V. R– 135 A Y – 188 A B – 167 A...
But the measured neutral current is only 18 Amps".

I have the following opinion, please advise.
1. Voltage is balance. Current is not. This big current difference can happen on a 3-ph Y system, with 1-ph unbalanced linear or non-linear load.
2. Note: A. For linear loads:
a) 3-ph balance loads, the Neutral current is Zero.
b) 3-ph unbalanced loads, Neutral current is NOT Zero. But the vector I1+I2+I3+I[sub]N[/sub] =0.
B. For non-linear (harmonic generating) loads:
a) 3-ph balance loads, the Neutral current is NOT Zero. The fundamental (frequency) current is Zero. The Neutral current = sum of harmonic currents.
b) 3-ph unbalanced loads, Neutral current is NOT Zero. The Neutral current = sum of harmonic currents + the fundamental (frequency) unbalance current.
3. The current reading R-135 A, Y-188 A, B–167 A, and N-18A, these are the [fundamental + the harmonics].
Note: Take the case say 3 non-linear balance loads, the fundamental current is Zero. The Neutral reads the harmonic currents, which is possible to be not very heavy. However, if the non-linear loads are unbalanced, the Neutral current is the [unbalanced fundamental frequency current + the Harmonic currents ].
Che Kuan Yau (Singapore)
 
How about single phase load, A-B, single phase load B-C, single phase load C-A.
The neutral does not need to be present to connect single phase loads phase to phase.
Unbalanced phase to phase loads will change the phase angles, but will not cause a neutral current.
The neutral only carries the unbalanced current from line to neutral loads.
Please check and report on single phase,line to line loads.
Some three phase equipment may have internal devices such as heaters that cause unbalanced line to line loading WITHOUT CAUSING ANY NEUTRAL CURRENT.
With single phase, line to line loads disconnected, your neutral current should be as expected.
Unbalanced line to line loading must be eliminated and the neutral current measured and calculated on the remaining line to neutral unbalance.

--------------------
Ohm's law
Not just a good idea;
It's the LAW!
 
Or, my favorite (?). Gotten calls from the field that transformer relay and the "multi-function meter" were showing radically different transformer neutral currents. Short story is that the MFM was displaying RMS current, a big number, while the relay was displaying fundamental current (a much smaller number). Apples and oranges...

When one this sentence into the German to translate wanted, would one the fact exploit, that the word order and the punctuation already with the German conventions agree.

-- Douglas Hofstadter, Jan 1982
 

In this case THD is 2.7% and difference in neutral current is >50%. There should be some other issue.
 
3 phase input RMS current waveform.
3_phase_current_waveform_onzmq4.jpg


3 phase input THD current waveform
THD_current_waveform_m6jnfk.jpg


Do you see much of a phase angle difference here?

There are no 400 V (RY, YB or BR) single phase loads.

Only 3 phase air conditioners, UPS for computer systems, LED lights, fans.

Muthu
 
I have the following opinion for your consideration. Please advise.
1. Base on the I[sub]rms [/sub] readings:
I[sub]Rrms[/sub] = 136.3A, I[sub]Yrms[/sub] = 188.2A, I[sub]Brms[/sub]=168.9A
Note: Irms = I fundamental (with 0, -120, -240[sup]o[/sup] angles)+ harmonics (without angle).
2. Base on the THD% R = 3.2%, Y = 2.5%, B =2.6%
3. Base on above 1. and 2., the fundamental f0 current I[sub]R0[/sub]= 136.24A /angle 0[sup]o[/sup], I[sub]Y0[/sub]= 187.25A /angle -120 [sup]o[/sup], I[sub]B0[/sub]= 168.84A / angle -240 [sup]o[/sup].
3.1 Note: Sum of 3 fundamental 120 deg apart currents with 1-phase loads on RN, YN, BN only = unbalance current = about 4.2A, . Excluding the Harmonic.
4. The actual current on the Neutral = unbalance current (4.2A) + the Harmonics.
4.1 Note: As the Harmonics are NOT very high, the Neutral current reads 18A is possible.
Che Kuan Yau (Singapore)
 
There are no 400 V (RY, YB or BR) single phase loads.

Only 3 phase air conditioners, UPS for computer systems, LED lights, fans.


There are line to neutral 230V single phase loads though, right? Otherwise, there should be no neutral current.
 
Edison123 said:
Do you see much of a phase angle difference here?
Note that B peaks considerably after the crossing of R&Y. This would occur if the angles of R&Y were 0 and -120, and the angle of B was 100 deg.

Try moving the cursor on the meter to determine the zero crossing times of the three currents.
 
Looking at the loading type, we should be asking what is the frequency of the neutral current? There maybe more harmonic than you expect. In the worst case the neutral can be up to three times any phase current.
LED lighting, and UPS systems can be very dirty switching power supplies that generate loads of harmonics.
As David said above, the current read on different devices can be a big clue.
 
Caveat. Today's readings at low loads of 40 Amps (not the previous ones).

Also, there is a voltage regulation problem from utility side (430 V on low load to 370 V on high load).

Current phasor (low load)

08._3_phase_current_vector_othktl.jpg


Voltage phasor (low load

07._3_phase_voltage_vector_jhym9i.jpg


Will post high load phasors later.

Muthu
 
Current phasor with full load

08._3_phase_current_vector_-_with_load_kgxru2.jpg



Voltage phasor with full load (75 to 80 V drop in voltage with full load. Utility has been informed about poor regulation)

07._3_phase_voltage_vector_-_with_load_ik0jjk.jpg



3 phase current THD on full load (not much)

12_-_Harmonics_-_Current_3_phases_-_with_load_eiixwg.jpg



Measured neutral current 16 Amps with Fluke clamp-on.


Muthu
 
What is the neutral current at low load?

--------------------
Ohm's law
Not just a good idea;
It's the LAW!
 
What do the angles phi_12, phi_23, phi_31 represent?
 