NickParker
According to ABS Building and Classing Marine Vessels (MVR) 4.8.2, clause 7.13.2, the normal and emergency lighting systems must be independent of each other and designed in such a way that a failure in one system does not cause the other to become inoperative.
Considering this requirement, how should the typical power distribution be configured to comply with the clause? Additionally, does the following arrangement meet the criteria?
We provide emergency lighting fixtures with integral battery backup:
1. Emergency lighting fixtures are powered by the Emergency Distribution Board.
2. The Emergency Distribution Board normally receives power from the Normal power source.
3. In the event of Normal power failure, the Emergency Generator activates and supplies power to the Emergency Distribution Board.
4. During the transition from Normal power to Emergency power, the integral battery within the fixture powers the emergency lighting fixture.
Does this configuration satisfy the requirements of the clause?