Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by Antifed

  1. Antifed

    Massachusetts Specialized Energy Code - Energy Recovery

    Something I used in a laboratory exhaust energy recovery design was from HPT (heat pipe technology).
  2. Antifed

    Changing from Glycol to Water Cooled Chiller

    Hi! Would you mind clarifying something for me? Are you converting a system that supplies chilled glycol to terminal units / equipment to one that will supply straight chilled water to those end point devices? Are you converting from an air cooled chiller to a water cooled chiller? Are...
  3. Antifed

    Equipment Heat Gains / Diversity During Winter

    I'd been taught to account for the extremes (i.e., assume the equipment load is not there to help you with heating). In reality, you heating mode may never turn on, but it is there if you need it.
  4. Antifed

    ASHRAE 62.1 Ventilation Rate Procedure (VRP) Question

    Which edition of the standard are you working with? I can check the guide book to see if ASHRAE has weighed in on this. If the offices are small compared to the laboratories AND they and the laboratories are ventilated from the same unit, I'd likely just call the whole thing a lab and be done...
  5. Antifed

    Chilled Water Buffer Tank - Primary/Secondary - Design Help

    Hi, Please forgive my peppering you with questions. Just for clarification, the existing set up is a compressor chiller, correct? As far as the buffer tank goes, and if you need it, what is your system volume and how much buffer does your Daikin require? Is system currently variable...
  6. Antifed

    Inlet Filter Pressure Losses

    See the following link for how your fan performance will change depending on your system's characteristics: https://integracontrols.com/fan-curves-explained/ Please see the below image for an illustration of what Snickster wrote.
  7. Antifed

    Trace TRACE 3D Plus - external supply air modelling query

    I highly recommend reaching out to CDS support for help in getting this set up. There may not be a dissect way to model your set up, but there could be ways to manipulate the system set up to approximate what you are trying to do. Also, version 7 of the software just came out so you may want to...
  8. Antifed

    Pump Corrosion

    I need to find out what they are putting into the system--thanks!
  9. Antifed

    Pump Corrosion

    It is a drain line for seal leaks or condensate.
  10. Antifed

    Pump Corrosion

    Maintenance certainly is lacking. The usual problem of building facilities and not funding/staffing up to keep them going.
  11. Antifed

    Pump Corrosion

    Hello, I was on a site visit the other day and came across this Armstrong Pump in the secondary side of a heating hot water system. There are no corrosive chemicals in the room nor anything outside of the boiler room that could be drawn in from the combustion air louvers. The maintenance...
  12. Antifed

    Sensible heat gain of electric motors

    Hello, How did you obtain the actual heat gain? Is that from the manufacturer's catalogue? My old (2001) ASHRAE Fundamentals Book shows the instantaneous heat gain from a 15-hp motor as 44,400-btuh based on F_um=1.0 and F_lm=1.0, with the motor and driven equipment being located within the...
  13. Antifed

    Ductwork Sizing for VAV Box System

    I've seen 0.08"/100' used for the distribution system and 0.1"/100' for downstream of the VAV box. What is the pressure drop you are seeing and what is it in the grand scheme of things? The 0.1"/100-ft is an equal friction value that, at one time, was based on a good balance based on economics...
  14. Antifed

    Fan/Blower Coils with DOAS

    ProcessHVAC, the unit would be more accurately described as a dedicated ventilation and dehumidification unit. I call it DOAS because the unit is the dedicated source of fresh air for the space. The recirculated air provides the extra volume needed to dehumidify the zones. I ran into an issue...