  1. argotier

    Current unbalance in 3 phase system but no neutral current

    Thanks, now I see it. I would check all the measuring circuit, something is wrong.
  2. argotier

    Current unbalance in 3 phase system but no neutral current

    First we should separate both aspects of your problem, on one hand the current unbalance and in the other the presence of harmonics. For the current unbalance part, as already said, not necessarily a phase current unbalance will result in a neutral current (only if the sum of the current...
  3. argotier

    Minimum power loss in a transformer

    You can always ask for a higher efficient transformer but be aware that it's cost will increase aswell, maybe considerably. I don't have USA references in this case (DOE 2016 does not apply here), but for your information, in IEC world (IEC 60076-20: Power transformers - Part 20: Energy...
  4. argotier

    how long can a 500 MVA transformer remain in a nitrogen-filled port for shipment in an aggressive en

    Weird... I thought I had already answered to this thread... [ponder] Here it goes again: Usual storage time for N2 filled transformer is around 3~6 months, depending on the manufacturer's instruction (which you should always refer to first). For longer periods it is recommended to fill with...
  5. argotier

    Sealed-Tank Design vs Conservator-Tank Design in 20MVA power transformer, pros & cons

    As both main designs are valid, I would go with the one more common in your country/area. That way you will avoid surprises later on with the installation, maintenance and eventual need for spare parts.
  6. argotier

    Transformer Dissolved Gas Analysis

    For a proper analysis you will need to consider all relevant gases and not only Ethane. I recommend you to check the following standards that will help you in interpreting the DGA results and identifying the problem (if any) or ruled it out: - ANSI C57.104-2019: IEEE Guide for the...
  7. argotier

    Transformer H0 connection and BIL rating

    If the neutral will be ungrounded, then you must consider a fully insulated wye, with same insulation for neutral and phase bushings (and fully insulated windings). In the standards is not so clear, because the statement is not of the form: When neutral ungrounded --> go fully insulated But...
  8. argotier

    Helpful advice please

    prc, good to know, I will check it out!
  9. argotier

    Helpful advice please

    Not a book, but a publication that always has something interesting to read: Transformers magazine
  10. argotier

    ANSI load tap changing transformers

    If it helps you to understand the switching sequence, yes it's something like that. Just be aware that the OLTC actual circuit is not like your drawing, for instance the OLCT doesn't have one switch per tap, but instead two moving contacts and only one set of switchs per phase. The two moving...
  11. argotier

    ANSI load tap changing transformers

    As prc said, for reactive type OLTC (usual for US), you will have a tap winding of +/-8x1.25% as the preventive autotransformer can be connected mid tap providing half tap voltages, increasing the total number of tap positions to the standardized +/-16x0.625%. So, in your example, the tap...
  12. argotier

    Vacuum Pressure Gauge on Free Conservator Tank Transformer

    Are you sure that the transformer is free-breathing type? It doesn't have a rubber bag or bladder inside the conservator? That's the only time I can imagine a pressure-vacuum gauge might be of some use (In IEC world these gauges are never used for transformers with conservator, with or without...
  13. argotier

    Organizational Charts

    To answer your question: If you are looking just the organizational chart (I mean the diagram), with some luck you might find some in the companies website. But I think is not the general case. To know more about a company structure and the interaction between its departments, you will need to...
  14. argotier

    Combining multiple CTs and dealing with bi-directional flow

    Very interesting. May I ask if the existing CT/PT are connected to the MV or the LV side? Energy meters take into account not only the currents but the voltages, if the PTs are connected on LV side of the transformers and you have to choose one for the exporting meter you may introduce some...
  15. argotier

    Impulse Generator for transformer testing

    Yes, you are correct. The impulse generator is used to test the transformer insulation withstand regarding voltage transients. In very simple terms, the generator charges a series of capacitors and then discharges them over the test subject when the charge level is right. Some resistors are...