I really appreciate your professional feedback. It appears that I made an error in saying synchronization of both sides using a coupled DC bus. Under normal operation, the DC outputs of the VFDs are interconnected through the contactor. In the event of a VFD failure, the operator will deactivate...
Thank you for your feedback!
On a bucket wheel reclaimer, there are two Variable Frequency Drives (VFDs) for the long travel drive motors: one for the left side and another for the right side. The client wishes to synchronize both sides using a coupled DC bus while operating the machine...
Hi,
I have two VFD 45kW, 600V, 3Phase, 60Hz. The DC bus of two VFDs are required to connect trough a contactor. What is the voltage rating of the contactor I should consider? Will 690V rated contactor suitable for this? Your comments is much appreciated.
Thanks,
Kani
Hi,
Do we need to protect the VFD braking resistor using fuses? If so how do I calculate the fuse rating? The braking resistor is 400W and 18Ohm, VFD output 600V, 3Phase, 60Hz. VFD rating is 45kW. I appreciate your feedback and help.
Thanks,
Kani
Hi,
Why we need to consider 1000V rated power cable for 600/347V Y system, solidly or resistance grounded. Your feed back is much appreciated.
Tanks,
Kani
Hi,
Can I use 15HP 460V 60Hz motor on 480V 50Hz System? What are the formulas to calculate FLA of this motor at 480V 50Hz. Please provide a calculation example.
Thanks,
Kani
Thanks all!
According to your replies and my search, I came to a conclusion
System N+1: N is required units and +1 will be standby. If one of N fails, the standby unit will kick on.
75kVA Generator Example: 3x 25kVA online and one 25kVA is standby. or 40kVA+35kVA online and another 40kVA is...
What i think n+1 shall have all units same. as per jraef ( 4 x 25kW). N-1 can be any combination. If any unit fails, non of other units shall be overloaded. example: for 75kVA requirement, we can use 40+40+35 three gen set in parallel. I think this is what Crshears means above. any comments?
Hi,
Can you please help me to understand the different between N+1 and N-1 redundancy. If the actual requirement is 75kW heater. What will be the combination for N-1 and N+1 redundancy system
Thanks