Recent content by OffTap100

  1. OffTap100

    How to increase lifetime of ceramic isolators on 66 kV line?

    Is it recommended to replace all ceramic isolators after years of use? Ours are in service since 2007 (14 years." Are they located in a area of heavy pollution? Heavy industry, cement plant/quarry etc? Although are system is slowly changing over our transmission and distribution to...
  2. OffTap100

    Utility Power Factors over the years

    TugboatEng Do you know of any articles, info, white papers etc ..regarding motoring decommissioned generators? Very interesting topic indeed. Grid level stuff. Increased voltage support at a grid level? or just vars? OT
  3. OffTap100

    What is Typical with Back-UP DC Wiring?

    Can you please explain your " back up DC system" ? Are you referencing something different then your standard station battery system for a sub? A bit confused....
  4. OffTap100

    Protracted Faults In Substations

    That was obviously more then just burning mineral oil after the fault was isolated. That was a looooooooong fault.
  5. OffTap100

    Do you delay tripping on low oil? How long?

    How low is your oil to begin with? I assume it has a nitrogen blanket?
  6. OffTap100

    Vacuum Pressure Gauge on Free Conservator Tank Transformer

    Is the gauge/valve located slightly above the conservator tank..or at the end of a pressure relief device? We have a few units where the pressure relief device is a 6" pipe that is mounted at an angle on top of the transformer, with an emergency glass blow out device. On top of that is a small...
  7. OffTap100

    Transformer ONAN Primary Fusing

    125% We have many(5) 66/15kv 15MVA+ single transformer substations that feed only one industrial customer. Fuses only on high side. Never had an issue, but I will say in most every case, the transformers are oversized a bit, for the current load. Rest of our subs/switch yards are...
  8. OffTap100

    Neutral Conductor in Medium Voltage Distribution

    NYC, Chicago, Cleveland etc..Com-Ed, Con-Ed. Basically most if not all OLD cities still utilize a lot or at least some Delta.
  9. OffTap100

    Testing 12kv rated capacitors

    I definitely have a Doble. That's why I am confused why they want us to do it in this manner. Just seems odd.
  10. OffTap100

    Testing 12kv rated capacitors

    Has anyone in this past century... applied 120v across 12kv rated individual capacitors, and measured the current? Engineer wants us to do that, in addition to checking capacitance using our Capacitance Meter. OffTap
  11. OffTap100

    Temp porcelain bushing repair kit

    Thank you. Glyptal is more of a sealant. Looking for more of a putty.
  12. OffTap100

    Temp porcelain bushing repair kit

    Need to temporarily repair a porcelain bushing skirt, until new is received. Over the years I have used different "epoxy style" products to accomplisj this, but all have been out of date and thrown away. Can anyone recommend a current product sold in the U.S.? Thanks
  13. OffTap100

    Meggering of Dry-type or liquid-filled transformers

    !000v for 600v transformers is the suggested megger voltage. Obviously transformers rated at a higher voltage require 5kv, 10kv and much higher.