  1. SandwichEngine

    PEMB buildings from China? Engineering?

    I'm a PEMB guy and I would run. One thing you want to look for with PEMB suppliers is that they are IAS certified. It's the same as being AISC certified for a conventional fabricator. They come in a few times a year and audit your engineering, business practices, and most importantly, shop...
  2. SandwichEngine

    Crane Side Thrust Loads

    The difference in load based on control type is due to speed. Pendant cranes go as slow as a man can walk. Cranes controlled from a control room (radio) go faster and therefore create a larger dynamic load. Cab cranes go even faster and therefore have even higher loads. These days most...
  3. SandwichEngine

    PEMB Shear Breakout

    I'm a PEMB guy. One thing I've seen a lot of foundation engineers get wrong is the direction of the shear wind loads on rigid frames. When you have vertical loads like dead or live, it pushes down on the rafter and the columns want to kick out. The opposite happens in wind loads due to high...
  4. SandwichEngine

    ASCE 7-16 Figure 30.4-1 Shaded C&C Wind Pressures

    Is there a chance that the book is working in ASD? If so, the minimum design-level load would be (16 psf)*(0.6) = 9.6 psf.
  5. SandwichEngine

    Reduction in Strength of epoxy anchors based on reduced anchor spacing

    I'm in a hurry but I believe the ACI code gives the required spacing but makes exceptions for products with tested values with closer spacing. If you free download Simpson Strong Tie anchor designer, I know it will allow about 4db for many of the epoxy anchors, depending on diameter. I presume...
  6. SandwichEngine

    built up beam

    You might find help in crane beam design resources. They are usually some type of built up section due to the need for strength in both directions. Crane-Supporting Steel Structures by R.A. MacCrimmon is a great resource with design examples. You can get it free. Just google Canadian crane...
  7. SandwichEngine

    Pre-engineered Columns for Compression

    Your results sound off to me. Are you considering the girts and flange braces as weak axis restraints for bending and compression?
  8. SandwichEngine

    PEMB frame deformation due to foundation settlement

    These things can bend a lot in their weak axis without yielding. If you can get it straightened out and nothing has yield line, then it's remained elastic. https://youtu.be/V7zOZbCQ94M?si=qPRy6IQNFzt9Jw8p I'm guessing a PEMB erector would be a good resource for how to get the rafters back to...
  9. SandwichEngine

    Another Structural Software Thread

    Tekla Structural Designer does #2 easily. Haven't needed number 1.
  10. SandwichEngine

    Door Frame Canopy Supported by thin Z-Girts

    These type of canopies are added to PEMB type buildings all the time without requiring any complex analysis. Lots of companies sell canopies like this "off the shelf" that are just installed anywhere on a PEMB building. Presumably, the off the shelf canopies are aluminum and very light. May...
  11. SandwichEngine

    Analyzing and code checking a pre-engineered metal building for new rooftop RTU loading

    I just want to discourage anyone from using photos from a storm and pointing at one example of a building failing close to others and making conclusions about entire building systems. I attended a research symposium a few years back where a professor studied building failures after Hurricane...
  12. SandwichEngine

    Fastner Pull Test and Steel Deck KSI

    If I'm reading your post right, you've performed tests where you pulled on a fastener until it pulled out and you got 530 lbs. For one, you check pullout using ultimate strength, not yield strength. For two, it depends on the diameter of the screw. That being said, assuming a 1/4 (#14) tek...
  13. SandwichEngine

    Analyzing and code checking a pre-engineered metal building for new rooftop RTU loading

    The odds of you getting it to work are low. I'm a PEMB guy and buildings we designed a few years ago wouldn't be shown to work for the newer wind loads. Not only has the wind loads gotten stronger according to the code, the wind maps are totally different. Because the IEBC required anything...
  14. SandwichEngine

    PEMB: 240k Kickout Tie-Beam

    240 kips? I'm a PEMB guy and that sounds crazy. I checked a 200 ft clear span hangar that we did recently and the largest lateral factored load is 74 kips ASD. So if you haven't already, either question that loading or figure out how it's so large. The biggest lateral loads on PEMBs are due...