Not sure what code you`re looking at, but IBC `15 section 1607.14 requires 5psf load on interior partitions.
Section 1607 covers live loads. This means 1) it's not a wind load, 2) it needs to be factored by 1.6 for LRFD combinations, and 3) the wind load deflection modification factor isn't applicable (table 1604.3 footnote f).
I`ve always thought about the 5psf as being a possible mechanic overpressure or as a possible errant wind gust so I`m not a huge fan of this reading of the code, but that it how its written.