I have an interesting dilemma in my utility plant. I currently have two vertical turbine cooling tower pumps, same model & vintage, that each have a vibration issue. The first pump is a 1.1 ips 1x vibration in one direction at the motor outboard. The second pump has a loud buzzing noise coming from the motor, .20 ips 53x vibration in all directions at the outboard.
We've been running the second pump out of fear that the first pump is too far above limits to safely run. However our pump maintenance contractor suggests that the second pump is much closer to failure, noting the loud buzzing noise and frequency of the vibration (he believes a bearing failure is imminent). The first pump is likely misaligned, and being a vertical turbine, it's understandable to see higher vibration on the unsupported end of the motor. Nonetheless, I'm resistant to running the first pump because of the high amplitude of vibration.
Thoughts?
We've been running the second pump out of fear that the first pump is too far above limits to safely run. However our pump maintenance contractor suggests that the second pump is much closer to failure, noting the loud buzzing noise and frequency of the vibration (he believes a bearing failure is imminent). The first pump is likely misaligned, and being a vertical turbine, it's understandable to see higher vibration on the unsupported end of the motor. Nonetheless, I'm resistant to running the first pump because of the high amplitude of vibration.