Good Morning All!
I've looked over the forums and have found some topics regarding one-way shear in a two way slab system however none cover the issue that I am currently facing. At my office we are currently having a debate among the structural engineers and was hoping I could get some more insight from anyone on the boards.
I am analyzing an existing concrete building that has a two way concrete slab system with capitals and drop boxes. My company is currently designing support steel that will be support new tank loads. The new support steel columns are located very close to the existing concrete columns (base plate is 1" off of the existing concrete column). I am doing calculations to check the transfer of this new load from the steel to the concrete columns and an issue has arisen regarding shear.
I know I need to check: (A) Punching shear of the new base plate with its respective critical perimeter, (B) 1-way shear in the slab system, & (C) 2-way shear in the slab system. I am using MacGregor's Reinforced Concrete Text and of course ACI. I understand that 1-way shear rarely controls in two way slab systems however in my new scenario it is. Thus the debate. I am dividing my loads from my tributary area over the entire width of the drop box for one way shear as discussed in McGregor's text (pg 586). For one way shear the critical distance is located at 'd' from the face of the column. If my new load from the steel column is within this 'd' then does this additional load contribute to the 1-way shear or does this action more or less act in 2-way shear (?even if it was outside 'd'?). I believe that I should consider this new load for both 1-way shear & 2 way shear action regardless if the load is located within our out of the 'd' critical distance (I am practically breaking it down to a concrete beam with a shear diagram at this point). What I am doing is getting a shear load per unit width and comparing it to the effective unit width of the new base plate. No where in the text nor code do I understand that if my load is within the critical distance, that I need not consider 1-way shear. Another structural engineer at my office is stating since I am so close to the existing column (within 'd') that 1-way shear need not be considered and the 2-way shear will be the controlling failure. I am having a difficult time validating this.
If I could get any help on this issue it would be greatly appreciated! Also, I have attached an image for further clarification.
Thank you all in advance!
I've looked over the forums and have found some topics regarding one-way shear in a two way slab system however none cover the issue that I am currently facing. At my office we are currently having a debate among the structural engineers and was hoping I could get some more insight from anyone on the boards.
I am analyzing an existing concrete building that has a two way concrete slab system with capitals and drop boxes. My company is currently designing support steel that will be support new tank loads. The new support steel columns are located very close to the existing concrete columns (base plate is 1" off of the existing concrete column). I am doing calculations to check the transfer of this new load from the steel to the concrete columns and an issue has arisen regarding shear.
I know I need to check: (A) Punching shear of the new base plate with its respective critical perimeter, (B) 1-way shear in the slab system, & (C) 2-way shear in the slab system. I am using MacGregor's Reinforced Concrete Text and of course ACI. I understand that 1-way shear rarely controls in two way slab systems however in my new scenario it is. Thus the debate. I am dividing my loads from my tributary area over the entire width of the drop box for one way shear as discussed in McGregor's text (pg 586). For one way shear the critical distance is located at 'd' from the face of the column. If my new load from the steel column is within this 'd' then does this additional load contribute to the 1-way shear or does this action more or less act in 2-way shear (?even if it was outside 'd'?). I believe that I should consider this new load for both 1-way shear & 2 way shear action regardless if the load is located within our out of the 'd' critical distance (I am practically breaking it down to a concrete beam with a shear diagram at this point). What I am doing is getting a shear load per unit width and comparing it to the effective unit width of the new base plate. No where in the text nor code do I understand that if my load is within the critical distance, that I need not consider 1-way shear. Another structural engineer at my office is stating since I am so close to the existing column (within 'd') that 1-way shear need not be considered and the 2-way shear will be the controlling failure. I am having a difficult time validating this.
If I could get any help on this issue it would be greatly appreciated! Also, I have attached an image for further clarification.
Thank you all in advance!