15kV Cable
JatTiw
47
Hi Every body
I am looking for Three (3) copper conductor, 350 MCM, 15 kV, 133% insulation level with semi-conducting thermosetting layer as well as metallic tape, cable with EPR (Ethylene Propylene Rubber) insulation, shielded and PVC jacketed, HL rating & flame test-rating FT-4, CSA approved, for installation in underground duct-bank & cable tray. Working Temperature +70o C to - 40o C.
Please suggest me manufacturer, can supply this type of cable
Thanks mpparent, do you have any contact info at Okonite
I would go to this web address:
That way you can find a local sales person in your area.
Mike
PS I believe they're mainly a US company, so I hope you're in North America.
... and Kerite, Hitachi, Southwire, General Cable, blah, blah, it's standard stuff. Only thing I'm not sure about is the low end of the working temperature range. -12C is commonly given as the minimum.
Pirelli also makes cables that have a strand blocking pompound that prevents water and gasses from traveling between the wire strands. Ordinary concentric stranded conductor acts as a poor excuse for a water or air hose. Compact stranded is an even poorer excuse.
Keep in mind that if your ambient temperature really will be as high as 70°C, the cable will have to be greatly derated.
Is there any problem for getting HL & FT rating for un-armoured cables also? Cause cable I am specifying un-armoured cables.
The references cited by others will cover un-armoured cable. What is HL & FT?
Doesn't working temperature have to do with the temperature at installation? Once it is underground and loaded, the cable itself would presumably not reach the extremes specified.
William
Hi jghrist,
HL rating is CSA designation for cables installed in electrically hazardous location (Class-1 Div/Zone 1 etc) & FT is fire test rating for cable comment,