Hi jacphi,
I think – in agreeable with jbartos- this is going to be another wrong application.
Zero sequence (Donut c/t) ct connection (50 GS) is normally used for high resistance grounded systems. Since the earth fault current is limited in the range of 2-5 Amp, on those systems, by having a very low secondary current in the c/t (50/ 0.025) it is possible to increase the sensitivity of the relay operation. Then it will respond even for very small earth leakage currents. If the donut c/t is connected in the “CORRECT” way by passing through it “ONLY” the phase conductors there is no reason for it to trip for spurious earth fault currents in the vicinity.
But if we use the same c/t on a solidly grounded system where we have got very high earth fault currents, it is possible to get the c/t saturated and hence the objective is lost. If you make a rough calculation for the possible earth fault current magnitude at the end of the motor cable with a 480 V/85 kA fault level at the feeding point, you will definitely end up with at least 60 kA with a reasonable LV cable length and size. Then what will happen to the 50/0.025 c/t when there is a fault of 60 kA at the cable end (motor terminal box)? For your information even if you refer the IEEE Buff book it strictly recommends to not to use zero seq. earth fault protection schemes due to similar reasons.
May I divert the issue in some other direction! ( 480 V/ 185 kW motor )
1) Are you going to open the LV motor contactor by this earth fault trip signal for an earth fault current in 60 kA range during an earth fault which is possible in your solidly grounded system?
2) Can the LV contactor break such a high fault rating?
3) Does the relay has the facility to block the earth fault trip command for a while till the motor LV main fuses or LV circuit breaker handles that high current and open the circuit?
Note: It seems to me that you are going to apply a motor control relay suitable for a 4160 V high resistance system on a LV contactor system.
Regards!
Kiribanda