I have a 350A neutral resistor for a 2MW generator, and I'm trying to determine size of neutral resistor cable. I used equation: (1/A)^2 *t = 0.0297*log[(T2-234)/(T1-234)], and came up with A=23,643 (t=10s, T2=150, T1=90). This means I can use #2 AWG cable. The phase conducts are 6-1/C #250 (2 conductors per phase). Does that seem correct?