A while ago, I started a thread which many of you contributed to, but that story has not ended yet...

So the issue is that a 3.5 MW motor driving a large fan has problems starting. The starting method is the soft starter. Rotational inertia is high.

We discussed several causes, such as inadequate motor, inadequate starter, week and inadequate power system, etc. But calculations show that although things are marginal this still should work, but it does not.

Today we managed for the first time to put two identical 13/20MVA transformer in parallel. Their impedance is 10.5% at 20MVA but each transformer also has a current limiting reactor 6%. However, 20+20MVA system still would no start a 4MVA motor...

System: two 13/20 MVA transformers in parallel, + about 5 MW of additional load shared between two transformers.

Motor: asynchronous, TECO-Westinghouse 3.5MW, In = 385Amp, 6kV, 50Hz, 1485 rmp, locked rotor current 2300Amp.

Fan: Large rotational inertia. The fan has no load at the present (no air, dampers closed). The Impeller weight is 15,000 lbs, and the Impeller moment of inertia (WR^2) is 66,000 lb-ft^2.)

Starter: constant current, voltage ramp ~10 sec, current limit 470%, starting time 50 sec, after which bypass contactor closes (when then speed is about 80%).

We had some luck starting and running the motor using one 13/20 MVA dedicated transformer but now with 2 transformers in parallel it would not work. We tried three times and none of the starts was successful. Each time the soft starter was manually shut down after about 20 sec since motor was creating too much vibrations and was not accelerating any more.

Problems still could be electrical, but for a change we started to suspect that there may be some mechanical problems, perhaps related to the motor rotor axial movement. If the rotor indeed does try to move, either it may not have enough space to move to the electrical center or the shaft is moving back and forth around its electrical center for some unknown reason and hitting the trust.

The attached charts provide more info. During the voltage rump time, which was about 10 sec, motor runs smooth and with two transformers in parallel the initial voltage drop is rather modest - falls from 6.4kV to 6kV. This is good news, with one transfomer we had much larger initial voltage drops. However, the bad news is that after the voltage is ramped up high enough that the current reached the preset limit (470% In), some vibrations start.

As you can see, the current and voltage outline forms on the charts start at some point having "teeth" like a saw. Once stabilized there is about 3 - 4 “teeth”/second. Just judging by the ear, the frequency of mechanical vibrations is in the same range, meaning current spikes likely correspond with frequency of mechanical vibrations.

Any idea what might be happening?
 
Replies continue below

Recommended for you

Interesting that the burn marks are seen only in between the fan blades. Did you send these to Teco ?
 
Not yet, will be opening another side and then will send them all pictures. As electricpete explained, this symmetrical pattern is more likely created electrically by some induced currents rather than "mechanically" by say hot air circulation. Seems that the fan blades somehow helped induced currents to form that symmetrical and uniform discoloration mosaic all around, where the symmetry of burnt segments was disturbed only if a hole happens to be part of a particular segment...
 
I think this fan is directly bolted on to the rotor shorting rings. If it is true, it's a bad design that could explain the heat marks.
 
After taking off the plate on the other rotor end, we found exactly the same situation - burnt paint on the rotor cooling fan (there are two identical fans on both sides of the rotor).

As per the attached picture, the way how the heat dissipation seems to works could possibly be explained like this:

1. The paint is still intact (not damaged) around any of the impeller blades. This could be an indication that blades are working as "coolers" conducting the heat away for the impeller plate.

2. Plate areas between the blades are apparently burnt as there is no blade to conduct the heat away.

3. Area between the blades where holes happen to exist too (whose purpose is unclear to me) are more badly overheated, perhaps due to heat conducting surface being reduced due to the hole?

Or maybe I'm completely misunderstanding this and some of you experts can make much more sense of this?

Even if things are as I tried to explain, it is still not obvious to me where that heat was coming from, and why. As electricpete explained, it more seems that the heat is generated due to induced currents, but why they are induced? Rotor damage is a strong possibility, but could it be as simple as due to such (possibly bad) design the stator windings which are partly around end rotor fans are inducing currents in the impeller in a "normal" way - same like currents are being induced in the rotor winding?
 
 http://files.engineering.com/getfile.aspx?folder=f09fd3e8-82d6-4648-b9ef-af1e777bb102&file=Rotor6.JPG
I was trying very hard to take a picture behind the end rotor fan, but not much success. Here is one where something is visible. Seems that whitish areas are rotor winsing slots (?). As per the manual (which is very poor and no details) rotor bars are not Al, but Cu, or some Cu alloy.
 
 http://files.engineering.com/getfile.aspx?folder=c4386c7b-d329-4d9a-bdfc-42373ee691a0&file=Rotor7.JPG
Yes, clearly the fans are bolted on to the rotor shorting rings. The whitish thingys are the rotor core pressure fingers, which keep the rotor core laminations in line and looks like these fingers have been burnt too. The red bars in between these fingers are the rotor bars, which are probably phosphor bronze.

Another interesting thing is that only the outer flange of the fan has burn marks but not the inner flange (one that is fixed to the rotor shorting ring), which kinda disses the circulating current thinking. Also, the fan blades themselves have no burn marks.

Can you unbolt the fans and remove them from the rotor shorting rings to take a gander at the bars and the rings ?

 
Good points by kumar (edison123).

I agree it is hard to explain how/why rotor damage would cause this particular pattern.

Less damage on inner flange than outer flange might possible be due to heat sink effect ters mentioned but I don't know... both the shorting ring and fan appear to "stand off" from the core/spider which is the main heat sink. We also notice the heating on outer flange is less directl above the fan blade... do we attribute that to heat sink effect or current pattern?

Another aspect was metnioned that the damage is symmetric (except for where the holes are). If it were rotor problem, I would have expected assymetric damage on the fan (more heating in areas of bad bars or damaged ring), but we don't see that.

(By the way the holes I would expect have something to do wtih balancing. Either they were drilled during trim balance at the factory. Or more likely they are provided so the client can easily bolt on balance weights if he chooses during subsequent field balancing of the rotor in situ.)

So the alternate scenario edison is suggesting is that these are currents created in the fan due to direct electrical contact with end ring which is said to be a bad design. What features in a "good design" prevent this? Maybe painted surfaces are supposed to serve as an insulator? I guess even if it is not a design problem, the fact that this motor has experienced many severe starts may make this type of heating more likely than some other motor with similar design that doesn't see those severe starts.

Final note - regardless of the source of this particular damage we still have lots of reasons to suspect rotor damage - namely the apparent slip frequency oscillations in current during start.

=====================================
Eng-tips forums: The best place on the web for engineering discussions.
 
it be as simple as due to such (possibly bad) design the stator windings which are partly around end rotor fans are inducing currents in the impeller in a "normal" way - same like currents are being induced in the rotor winding?
Fluxes in the endwinding area are much more difficult to predict and much more complex than in the slot section where we break it into a simple 2-d problem. So it is tough to say what is going on with the fluxes. However a big factor is that the iron core does not extend to this area so the magnetizing flux tends to be a lot lower here than in the slot section. Additionally the flux in this area tends to want to be leakage flux which encircle the conductors that created it, rather than travelling radially inward. Whether the conditions are ripe for inducing large currents in the fan I can't say. But I think a 2-flange fan like this is pretty common.

=====================================
Eng-tips forums: The best place on the web for engineering discussions.
 
Is he fan a magnetic material? If so, the heating may be a combination of all of the above;
Possibly:-
Due to current sharing with the shorting ring.
Due to induced magnetism from the end turns. Yes, I know that the field is supposed to be much weaker with no iron, but what about the magnetic material of the fan?
End play. The end play may be letting the fan move part way into the stator core.
The heating damage may be an indication of severe duty as a result of failed starts.
Is the end play in such a direction as to allow the fan to enter the stator core?

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
pete

I don't understand how this fan would work. Does it suck air from the rotor through the the big ventilating holes in the rotor core (in which the case there must be a baffle in the axial middle of that core and there isn't any) or does it suck from the winding overhang end (in which case it just seems to recirculating air in the winding over hangs (since it is delivering the air back to the winding overhangs) ? Why those big holes in the outer flange when they have a series of threaded holes in the inner flange for trim balancing ? And the million dollar question, why the burn marks ?

bill

Given the welded blades, it is a steel fan and hence magnetic. And given the thickness of the rotor shorting ring (at least 3 inches ?), there is no way the rotor would have that kinda end play.

 
Gents, thank you all very much again.

After taking a closer look it seems that holes around the outer fan plate are actually access holes to stick through a 13mm socket to unbolt the fan from the connecting ring, or whatever it may be attached to. But unbolting the fan(s) is a bit challenging. For one at the front, it is probably possible, there is enough access, however bolts are secured by welding touch and I'm not sure how easy would they would break lose. At the back of the motor, not much access since there is a large stator cooling fan at the shaft end working a a part of the heat exchanger. There is some room between the stator cooling fan and the motor body at the back where the inspection plate is, but not enough to get inside (sufficient to stick in you hand with a camera).

When coupled, there is no that much end play so the rotor does not really move more than 5mm away from the magnetic center. Whichever direction it moves, it brings one fan closer to the stator core, and the other fan further away. I'm also not sure what these two fans are exactly doing, but looks like one is puling some air through the endwindings from the heat exchanger area sitting on the top of the motor, and then the air passes through the hollowed rotor and being pushed out by another fan through the other end winding?

This motor was probably started about 60 times so far, each time the start (successful or not) lasted 10- 50sec. Therefore, the total time when the stator current was in the range of 1500-2000Amp is about 30 minutes. If both fans worked as some soft of "extension" of rotor windings carrying high induced current, the time there were exposed to such torture was likely long enough to develop some burns...

Another picture of the ring area is attached. Seems that there was some overheating there too, but hard to say, the picture has a lot of “noise”, so not sure what is a real discoloration and what the noise...
 
 http://files.engineering.com/getfile.aspx?folder=24355520-f95a-4ca0-ac02-dc1d3328c405&file=Rotor9_(r).JPG
Good catch on those big holes in the front flange. Indeed, they are for remvoing the fan fixing bolts.[hammer]

But, tack welding the bolts kinda defeats the very purpose of these holes. Guys at Teco must be wonderful engineers.
 
Hello, everyone!
A lot of people claim that Eng-tips forum is great place and this treat is one of the good demonstrations.
My office is less then 1 km away from the facilities but I ,through Eng –tips, first time heard that Mr. Ters opened the motor and looked into!
Unfortunately I can't open the photos at my home and I will see rotor tomorrow morning.
Like Mr. Ters said, I am, temporary, just the Client but, in the future, I vill be, one of the people, who care about motor, 6kV netvork, protective releys, ECT.
In this project, people who work on were not generous. Recently I have come across the fan curve and I have seen that it need BHP of 4650 HP or 3500kW with the dampers 100% open and I saw, when system worked that motor draw nominal current.
On the other hand, many information and recommendation for heavy application like this call for minimum 10% - 15 % more motor power above BHP required for the fan.
With bigger motor and better rotor design I and Mr. Ters would be more peaceful person, but it is not worth crying over the spilled milk....
 
This being said... If the bolts are attached directly to the connecting ring, and have good galvanic connection with the ring, could then bolts be suspected to help additional (perhaps unwanted) flux to develop around their heads, which, for some reason, tends to go through the hole inducing so circulating currents which help burn the paint?

But this is rather an academic question... Even if I'm right, this provides no explanation why the motor does not start :)
 
My dear Client... As you know, during last 3 month there were more people around the motor trying to solve this problem than the rotor has bars :). But, it was only last Friday, when I finally asked myself what was the purpose of the plate at the motor end... being so the first one in that large crowd to realize it was an easy-to-remove inspection plate... with a slight delay though... [hammer].. We talked to TECO many times but they never said that inspection plates existed and should be removed to look inside... I e-mailed you pictures...
 
Did you try running the fan with the dampers closed ?

You could dedicate each start to those people around the motor. :)
 
Yes, damper are always closed during the start, or almost closed.

Did you mean name each start after someone hanging around :)
 