If you change the setpoint of only one droop governor of a parallel set, that will affect the throttle setting and the amount of load that generator picks up.
Mr. Che;
It was a long time ago, but I remember running three generators on a floating fish processing plant.
One generator would have been lightly loaded.
However, when the large refrigeration compressor started automatically, it took all three sets to carry the starting surge.
With only one or two sets online, the generator breakers would trip and the vessel would go dark.
On a ship, when the Captain needs the bow thrusters, he needs them now.
No time to ask;
"Are there enough generators online?"
CR;
Change KW sharing by changing the throttle setting. This may be done with a droop governor by changing the frequency set point.
Change KVAR sharing by adjusting the voltage on individual sets.
OP said:
Is it also a case where tow of them might be in droop and one is at isochronous?
Highly unlikely.
With one set in isochronous, the iso set will act as a swing set and compensate for any changes in load.
With a load increase, all sets will share the increase.
Then the iso will become active and the iso set will pick up the load increase and the droop sets will return to their original load levels.
The only time when the loads will be equal on all three sets is when the load happens to be tree times the load setting on the droop controlled sets.