Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

3 Generator Load Sharing Question

Status
Not open for further replies.

ThePunisher

Electrical
Nov 7, 2009
384
0
0
CA
HI all,

In one the facilities of our system, I can help notice this and took a photo.

All three generators are running under-loaded and the power factor is 1.09 of one and around 0.50~0.51 on the other two. If these generators are running in load sharing mode, why are their kvars or kVA not equal?

This is for my educational purpose only.

Regards,
 
 https://files.engineering.com/getfile.aspx?folder=556534b1-6e45-496e-a01e-14284219b2cc&file=Generator_Control_HMI.jpg
Replies continue below

Recommended for you

The fist approach for this is taking DG3 offline and check the offline voltage and compare this value with the data sheet. This voltage check should be done with a multimeter with a least 2 decimal place.

IF you can post a picture of the AVR and generator controller schematic.

Regards,
JS.
 
Status
Not open for further replies.
Back
Top