345kV GIS UG Connections

Status
Not open for further replies.

cyriousn

Electrical
Jul 19, 2017
18
Has anyone ever seen a 345kv GIS underground connection where two sets of conductors are paralleled into the same position? I believe this can be done with AIS equipment based on my review of some substations in NYC but didn't know if it was possible with GIS. I have the question going into some vendors but figured I'd ask here as well. Thank you!
 
Replies continue below

Recommended for you

I heard back from a vendor and they confirmed this is possible.
 
Status