Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

345kV GIS UG Connections

Status
Not open for further replies.

cyriousn

Electrical
Jul 19, 2017
18
0
0
US
Has anyone ever seen a 345kv GIS underground connection where two sets of conductors are paralleled into the same position? I believe this can be done with AIS equipment based on my review of some substations in NYC but didn't know if it was possible with GIS. I have the question going into some vendors but figured I'd ask here as well. Thank you!
 
Replies continue below

Recommended for you

Status
Not open for further replies.
Back
Top