I have a 3V0 (broken delta) resistor sizing question…
We have a 4160V, 1388kVA generator connected to a step-up transformer using a short distribution line (approx 3800 feet). The generator has a HRG system on it.
The distribution line is at 4160V and is configured as an ungrounded delta.
We put a set of PTs on the distribution line to detect ground faults. The PTs are connected wye (grounded) on the primary and broken delta on the secondary. They are rated 4200/120V and 1000 VA each.
I’ve read that it may be a good idea to connect a resistor across the broken delta to diminish the effects of ferroresonance. Following the calculation methods of an application guide, I came up with a maximum voltage (under fault conditions) on the resistor of 206V. Wanting to limit the current so as to not over-duty the 1000 VA rating of the PTs (using the continuous current rating, as it may be a while before the fault is cleared) I calculate a max current of 8.33 Amps.
To achieve the 8.33 Amps, I calculate that I’d need a 24 Ohm resistor (minimum) with a power rating of 1,715 Watts.
My question is… why not increase the resistance significantly and limit the power requirements of the resistor?... for example, why not use a 100 KOhm resistor with a 1/2 Watt rating, which would be much cheaper and easier to find?
Thanks in advance.
I have a 3V0 (broken delta) resistor sizing question…
We have a 4160V, 1388kVA generator connected to a step-up transformer using a short distribution line (approx 3800 feet). The generator has a HRG system on it.
The distribution line is at 4160V and is configured as an ungrounded delta.
We put a set of PTs on the distribution line to detect ground faults. The PTs are connected wye (grounded) on the primary and broken delta on the secondary. They are rated 4200/120V and 1000 VA each.
I’ve read that it may be a good idea to connect a resistor across the broken delta to diminish the effects of ferroresonance. Following the calculation methods of an application guide, I came up with a maximum voltage (under fault conditions) on the resistor of 206V. Wanting to limit the current so as to not over-duty the 1000 VA rating of the PTs (using the continuous current rating, as it may be a while before the fault is cleared) I calculate a max current of 8.33 Amps.
To achieve the 8.33 Amps, I calculate that I’d need a 24 Ohm resistor (minimum) with a power rating of 1,715 Watts.
My question is… why not increase the resistance significantly and limit the power requirements of the resistor?... for example, why not use a 100 KOhm resistor with a 1/2 Watt rating, which would be much cheaper and easier to find?