I'm trying to use water medium instead of glycol in waterside of cooling coil due to it is not sure if any impact of glycol to the air side. Does it work for using a heat exchanger to provide 1.5 degree C chilled water for low temperature dewpoint coil loop design without glycol added?
 
Replies continue below

Recommended for you

Glycol will increase parasitic losses over water.

Use propylene glycol if you are afraid of toxicity.
 
Is propylene glycol approved by FDA in the food manufacture application?
 
Some propylene glycol is food grade, and some isn't. You'll have to ask the propylene glycol supplier.

Best to you,

Goober Dave

Haven't see the forum policies? Do so now: Forum Policies
 
Is it possible to design the without any antifreeze of 1.5 degree C chilled water system for AHU'S cooling coil in practice?
 
in practice 4 degrees C is considered freezing threshold.
 