- Jan 29, 2008
- 1,052
I wonder if you motor gurus could give me a few pointers.
We have a project in China (50 Hz) where we are installing a 200 kW pump. We want to run the pump on a VFD somewhere between 3000 and 3600 rpm.
The pump will draw ~ 200 kW right at the point where the client specify changing from 380 V to 10 kV
Q1) Should we be selecting a 60 Hz motor and underspeeding it or a 50 Hz motor and overspeeding?
Q2) Would the 50 Hz option be the same HP motor as the 60 Hz option?
Q3) If you overspeed a 50 Hz motor does the Voltage go over as well or would we set the VFD for 380 Volts at the new top speed?
Q4)Would a 10 kV 200 kW motor be the same frame size as a 380 V motor?
Q5) What is the relevent cost of a 10 kV motor v/s a 380 Volt one?
Thanks in advance for the help.
Regards
Roy
We have a project in China (50 Hz) where we are installing a 200 kW pump. We want to run the pump on a VFD somewhere between 3000 and 3600 rpm.
The pump will draw ~ 200 kW right at the point where the client specify changing from 380 V to 10 kV
Q1) Should we be selecting a 60 Hz motor and underspeeding it or a 50 Hz motor and overspeeding?
Q2) Would the 50 Hz option be the same HP motor as the 60 Hz option?
Q3) If you overspeed a 50 Hz motor does the Voltage go over as well or would we set the VFD for 380 Volts at the new top speed?
Q4)Would a 10 kV 200 kW motor be the same frame size as a 380 V motor?
Q5) What is the relevent cost of a 10 kV motor v/s a 380 Volt one?
Thanks in advance for the help.
Regards
Roy