jchi
Structural
- Aug 21, 2006
- 27
I am checking an existing (25-year old) seed corn tower supporting (4) surge bins. The problem I have is that I cannot get the existing support beams to check out. They fail under flexure at 150% using 36ksi steel. If I check with 50ksi they just barley work 103%. However, I do not believe (no drawings) 50ksi was that readily available 25-years ago...
These beams also support the 4" thick concrete surge bin roofs/upper floor. I typically design these floors for 100 to 125psf (IBC - light manufacturing). They are typically only used for equipment access. We typically classify these seed toweres upper floors as equipment access to keep overall structure sq footage down trying to avoid sprinklers.
Does anyone else work on the these seed towers, if so what do you use for your upper floor live loads? 125psf seams heavy, 60psf seams light. I would prefer 100psf and use that for a minimum. However, the code has no good classification for seed towers.
Thanks,
Jeff
These beams also support the 4" thick concrete surge bin roofs/upper floor. I typically design these floors for 100 to 125psf (IBC - light manufacturing). They are typically only used for equipment access. We typically classify these seed toweres upper floors as equipment access to keep overall structure sq footage down trying to avoid sprinklers.