An 8 x 15 MW diesel plant is proposed as the only power source for a large industrial facility (no grid). The proposed generation voltage level is 11 kV which may be used to feed some large motors directly, or will be stepped down to other medim and low voltage levels to feed other loads, as needed. The plan is to connect all units to the same 11k V bus, no sections. Diesel machines would be some medium speed units.
What would be the most optimal configuration for dealing with high short circuit levels in this case? One of the proposed options would be to use step up transformers for each unit, bring the voltage up to 33 kV and then step it down to whatever various medium and low voltages will be needed in the process throughout the plant, introducing so additional impedance in the system what obviously will be much costlier.
This would also minimize transmission losses and cable sizes, although most large loads will be close to the power plant (within 200-1000 m) but few may be as far as 5 km away.
There are other propositions such as employing IS current limiters or having generator voltage 11 kV but with each unit having a step down transformer to introduce some impendence and to bring the voltage down to say 6 kV at which level most large motors could operate.
What would be the most optimal configuration for dealing with high short circuit levels in this case? One of the proposed options would be to use step up transformers for each unit, bring the voltage up to 33 kV and then step it down to whatever various medium and low voltages will be needed in the process throughout the plant, introducing so additional impedance in the system what obviously will be much costlier.
This would also minimize transmission losses and cable sizes, although most large loads will be close to the power plant (within 200-1000 m) but few may be as far as 5 km away.
There are other propositions such as employing IS current limiters or having generator voltage 11 kV but with each unit having a step down transformer to introduce some impendence and to bring the voltage down to say 6 kV at which level most large motors could operate.