strucguy
Structural
- Mar 20, 2007
- 235
A truss designer on the project I am overseeing is trying to convince me to not make them consider the weight of partitions in their truss design based on the following excerpt from TPI publication. Has anyone run into this issue before?
ANSI/TPI 2002, Section 2.2.5, “The weight of non-bearing partitions shall be permitted to be ignored for truss design purposes given the following conditions; if the following conditions do not exist, the Building Designer shall specify in the structural design documents the non-bearing partition loads that need to be applied to the trusses:
(a) Trusses are not spaced over 24 inches on center;
(b) Top chord panel length of supporting trusses does not exceed 30 inches;
(c) Design live load of supporting trusses results from a residential occupancy and is not less than 40 psf;
(d) Partition weight does not exceed 60 pounds per lineal foot; and
(e) When partitions parallel to supporting trusses are not located on or immediately adjacent to a truss, the sub-floor shall be of adequate strength and stiffness to support the partition load, or other provision shall be made to distribute the partition weight to the supporting trusses.
The truss layout for the project satisfies all the conditions above, and the designer wants to ignore the partitions loads in their truss designs. But, I am not sure if this is in compliance with the building code. Your feedback is greatly appreciated.
Thanks.
ANSI/TPI 2002, Section 2.2.5, “The weight of non-bearing partitions shall be permitted to be ignored for truss design purposes given the following conditions; if the following conditions do not exist, the Building Designer shall specify in the structural design documents the non-bearing partition loads that need to be applied to the trusses:
(a) Trusses are not spaced over 24 inches on center;
(b) Top chord panel length of supporting trusses does not exceed 30 inches;
(c) Design live load of supporting trusses results from a residential occupancy and is not less than 40 psf;
(d) Partition weight does not exceed 60 pounds per lineal foot; and
(e) When partitions parallel to supporting trusses are not located on or immediately adjacent to a truss, the sub-floor shall be of adequate strength and stiffness to support the partition load, or other provision shall be made to distribute the partition weight to the supporting trusses.
The truss layout for the project satisfies all the conditions above, and the designer wants to ignore the partitions loads in their truss designs. But, I am not sure if this is in compliance with the building code. Your feedback is greatly appreciated.
Thanks.