I'm having a problem with an AB Micrologix 1000 program that utilizes a sequencer (SQO) to alternate the operation of a series of lights. I'm fairly new to PLC's, but I understand ladder logic and have been successfully modifying previously-created programs as needed for new applications. I want to revise an existing program that sequences five lights(SQO Length=5) to one that sequences six(SQO Length=6). The original Length 5 program works fine. But in the Length 6 program, the output bit for position six never gets set, so the sixth light is never turned on.
Any suggestions out there?
 
Replies continue below

Recommended for you

If you could post your code, it would be easier to help.

There are several possible causes to your poblem.
1. SQO moves 16-bit data from one memory location to a word address, do you have the correct word in the source location?

2. SQO has a bit mask feature, perhaps you are masking the 6th bit. Is anything entered in the mask box? If the mask box has a file location instead of a hexidecimal value, you must have a mask word for each index, the mask file indexes with the source file.

3. Is the proper length been set? What is the current value?

 
Thanks for the help. We found the error in the source file. The sequencing works as expected now.
 