MNach
Structural
- Jan 30, 2015
- 18
I have a hanging bridge crane that is connected to an existing concrete structure using expansion anchors. Holes were drilled for these anchors and many hit existing reinforcing before making the required depth. I have contacted a Hilti rep for guidance on this issue and they said that they have not performed any tests on situations like these but provided me a test from the 80's (attached) that came to some conclusions, but also didn't say that Hilti accepts those conclusions (to cover his butt) and that the best way would be to treat the hole as an edge or an anchor and use the appropriate spacing. In another thread I also found the following link that Simpson did on this situation: Link. This study just outlined its conclusions while providing very limited data.
Does anyone have any experience or witnessed any issues with placing an anchor near (min. 2 diameters away) an abandoned hole? I am currently using Hilti's HDA-T M12 anchor to its full capacity (tension and shear) and have very little wiggle room to work with before these failed holes. Both studies appear to say that if the hole is filled and a minimum spacing of 2d is met, there should be negligible effects on the capacity. It's concerning though that few tests have been performed on this and that Hilti has no guidelines, mainly don't want responsibility. Does anyone know of any other tests that have been done on these conditions?
Does anyone have any experience or witnessed any issues with placing an anchor near (min. 2 diameters away) an abandoned hole? I am currently using Hilti's HDA-T M12 anchor to its full capacity (tension and shear) and have very little wiggle room to work with before these failed holes. Both studies appear to say that if the hole is filled and a minimum spacing of 2d is met, there should be negligible effects on the capacity. It's concerning though that few tests have been performed on this and that Hilti has no guidelines, mainly don't want responsibility. Does anyone know of any other tests that have been done on these conditions?