Absolute Noob Emergency Stop Controller Question

Status
Not open for further replies.

Eng8492

Electrical
Feb 25, 2013
27
I am using an emergency stop controller. When the emergency stop control is triggered, the output from the control should open a 2 pole contactor carrying split-phase 240VAC and a 3 pole contactor carrying 3ph power. Because I cannot find an e-stop control with any pilot duty ratings (ie UL508 Axx, Bxx, Cxx) which guarantees it can drive the contactors directly, I was planning on using pilot duty relays in between the controller and the contactors. Is there any problem with this approach?--safety requirements are minimal-- ie IEC Sil Level 0). Basically the customer just wants a visible E-stop function.
 
Replies continue below

Recommended for you

Why not just use breakers with an Under Voltage Release and run a voltage circuit through normally closed contacts of the E-stop? When the E-stop is pressed, the voltage is interrupted and the breakers open.
 
I think that is an alternate solution if the voltage through the Estop buttons is within the rating of the switch AND is non-hazardous. But now, instead of picking out an Estop controller, I have to check out those two factors and search for undervoltage breaker. Then paint the breaker handle green and make it externally accessible with a restart label...too much for my application. Great idea though.

Since I have posted this, I have done much research and learned that this approach is acceptable for some categories of protection. The universal recommendation is that any relay or contactor used to augment the voltage/current/isolation rating of the safety controller's contacts is performed with force-guided contactors or force-guided relays.

Force-guided relays/contactors cannot have any poles in a mismatched state. I am not sure what the purpose of this requirement is, if someone could treat this as my second question.
 
How big are these contactors and what are the coil requirements? The E-stop buttons I use have heavy duty contacts capable of directly operating the coils of most typical contactors in use.
 
Thanks for your interest Lionel. The total load is 3A to guarantee pull in. Im looking for a din rail transorb to prevent arcing.
But I am going to use the controller because it implements e-switch contact monitoring, voltage monitoring, and manual restart with a minimum of wiring.
 
My personal preference is to make e-stop circuits as simple as possible. I want to know they are going to work when needed. Your original approach will work, but look at the number of devices you are adding to this system with a controller and additional interposing relays. On the larger motors I work with with electronic motor protection relays, I let the relay handle almost all starts and stops, such that everything is an input into the relay and all logic is done inside the relay. The one function I don't wire through the relay is the e-stop. I wire a contact off the e-stop into the relay to record this action, but I don't want a problem occuring that prevents a motor shutdown and use hardwire contacts off the button in the coil string to guarantee shutdown. I would agree with Lionel that the good, old simple mushroom head button is a good solution to e-stop.
 