Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations The Obturator on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

ACC conductor

Status
Not open for further replies.

ATIFABDEEN

Petroleum
Jul 11, 2016
1

is it possible to use ACC conductor with 11/6.35KV with 33/19 KV system
 
Replies continue below

Recommended for you

Did you mean AAC or possibly ACCC conductor?
ACC is a signal cable supplied with end connectors and used to, among other things, trigger remote camera flash units.
ACCC and AAC are bare conductors and as such are not rated for voltage.
Some constraints are:
Rating of the existing insulators.
Spacing of the existing insulators.
Corona effect. Some references give 30 kV as the threshold for corona subject to other conditions. However, corona is rarely an issue at 33 kV.
[URL unfurl="true" said:
http://www.velco.com/library/document/download-migrated/Transmission%20Line%20Corona.pdf[/URL]]Corona occurs on all types of transmission lines, but it becomes more
noticeable
at higher voltages (345
kV and higher).

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor