PostFrameSE
Structural
- Sep 5, 2007
- 174
I am considering setting a new building on top of an existing foundation. It is 18" in the ground, 12" above ground, 6" wide, and has no footing underneath it. The overall dimensions then are 6" x 30" per lineal foot. Using 150psf, I calculate my dead weight at around 190plf. Conservatively, the current building setting on this foundation may weigh approximately 400plf. So I have around 600plf dead weight per lineal foot.
I took my load cell, screwed in a Simpson Titan HD screw and yanked on this thing with a piece of equipment. I did this twice and got around 6.0kips.
How can this be, without moving the entire foundation? What I don't know is if this thing is tied to the slab on the inside. Even if it was, under those loads I would expect some cracking, and there was none on the floor.
The fastener failed by pulling the screw right out of the hole.....the threads couldn't hold........not a cone failure.
What am I missing? I suspect there is some reinforcing in this concrete. How many lineal feet would it be reasonable to suspect is contributing to this uplift such that I can get so much more uplift resistance than I expected? And then.....what reasons do you give a building owner that despite not being below frost level (building hasn't heaved in 40+years) and the uplift resistance doesn't "calc out" that I'm not comfortable sitting on that foundation even though we did a "live" test and it carried three times what the design loads would be?
Would anybody set on something like this that you've actually load tested to be 2-3 times the design load?
Thanks.
I took my load cell, screwed in a Simpson Titan HD screw and yanked on this thing with a piece of equipment. I did this twice and got around 6.0kips.
How can this be, without moving the entire foundation? What I don't know is if this thing is tied to the slab on the inside. Even if it was, under those loads I would expect some cracking, and there was none on the floor.
The fastener failed by pulling the screw right out of the hole.....the threads couldn't hold........not a cone failure.
What am I missing? I suspect there is some reinforcing in this concrete. How many lineal feet would it be reasonable to suspect is contributing to this uplift such that I can get so much more uplift resistance than I expected? And then.....what reasons do you give a building owner that despite not being below frost level (building hasn't heaved in 40+years) and the uplift resistance doesn't "calc out" that I'm not comfortable sitting on that foundation even though we did a "live" test and it carried three times what the design loads would be?
Would anybody set on something like this that you've actually load tested to be 2-3 times the design load?
Thanks.