Takket3
Mechanical
- Apr 28, 2016
- 21
I have a 100% water chilled water plant that is going to get new chillers and be filled now with a 40% propylene glycol solution.
I need to check the existing cooling coils on the AHUs to make sure they are adequate to meeting the cooling load with the reduced capacity.
I know from the manufacturer's specific heat data that our Btu/hr = 500 * GPM * dT formula changes to 456 * GPM * dT
But, what about thermal conductivity? Do I need to factor that in? The thermal conductivity of water is 0.336 (BTU/hr*ft^2)(degF/ft). The glycol solution is only .215. Won't this further degrade coil performance?
I need to check the existing cooling coils on the AHUs to make sure they are adequate to meeting the cooling load with the reduced capacity.
I know from the manufacturer's specific heat data that our Btu/hr = 500 * GPM * dT formula changes to 456 * GPM * dT
But, what about thermal conductivity? Do I need to factor that in? The thermal conductivity of water is 0.336 (BTU/hr*ft^2)(degF/ft). The glycol solution is only .215. Won't this further degrade coil performance?