still not convinced.
according to the lit. new masterpact breakers are designed to meet IEC 947-2
this is taken from page 10 of the attached document
______________________________________________________
IEC 947-2 & BS EN 60947-2
This standard replaces IEC 157-1,
applicable since 1973.
The circuit breaker selection criteria remain
unchanged, but the new standard provides
the user with a better guarantee concerning
quality and performance.
Circuit breakers are now subjected to tests
that are more representative of real
operating conditions.
Icu : the ultimate breaking capacity,
which must be greater than or equal to
the 3-phase short-circuit current at the
point of installation of the circuit breaker,
a value unlikely to be reached under real
conditions;
Ics : the service breaking capacity,
generally expressed as a percentage of
the ultimate breaking capacity (25, 50, 75
or 100 % of Icu). It corresponds to a
short-circuit current that is more likely to
be reached under real conditions. The
circuit breaker must continue to operate
normally after having interrupted a
current equal to Ics three times;
All Masterpact circuit breakers have a Ics
value equal to 100% of Icu.
_______________________________________________
so that tells me that a masterpact should be able to handle a fault of (100Kaic in this case) 3 times
Ohm's it not just a good idea, Its the law.