Lubos

Mechanical
Feb 2, 2005
2
What are the potential problem with locating air cooled condenser (R407C) bellow level of compressor and evaporator. Approximatelly 3m. I can see potential problems with pushing liquid out of the condenser, oil circulation and maybe flashing off gas? How can you avoid those problems? Thank you.
 
Replies continue below

Recommended for you

This can be made to operate with appropriate control valves, and Parker Hannifin has a couple of arrangements in the Refrigerating Specialties application manuals about just this topic. There is a minor penalty in that the control valves are not set to manage LOW head pressure as normal in a larger system but to manage pressure at All Times; and of course the HP liquid line pressure is always appreciably lower than the condensing pressure.
 