I hope somebody can explain how to calculate the following problem to me. Here we go

I have an air duct approx. 2ft by 5ft. the duct has an airflow of 2500CFM. I have a constant 27 degree C air coming into the duct and a 1kW heater element in the middle of the duct. What will be the temperature of the air leaving the duct. If the air entering the duct increases to 32 degrees C, what will be the temp of the air leaving the duct. Thanks for the help
 
Replies continue below

Recommended for you

You are not allowed to post homework questions on the forum. But I will help you out anyway.

Q [BTU/hr] = 1.08 x CFM x (delta Temp)
Delta Temp = Q / (1.08 x CFM)

Change the electric heater capacity to BTU (1KW = 3412 BTU)

Delta Temp = 3412 / (1.08 x 2500) = 1.26 deg

Entering air temp = 27C / 32C
Leaving air temp = 28.6C / 33.6C

----
A green thought..."We don't inherit the earth from our ancestors, we borrow it from our children." (unknown)
 
MintJulip, thanks for pointing that out.

For some reason I thought delta T applies to any temperature scale.


----
A green thought..."We don't inherit the earth from our ancestors, we borrow it from our children." (unknown)
 
Thanks for the help and, no this was not homework. I am determining the root cause of some electronics failures in our equipment and I needed to validate my statement to the company that extreme temperature rise was not the cause. Thanks to your help I feel confident in my statement.
 
1.1 is a better factor and 1.24F is the temperature rise.
If 1.08 is considered then the temperature rise is 1.26F.

TADiep,

Get your hands on Uconeer from and you will have even temperature difference conversion in it.
TD of F varies by 9/5times TD of C.
 
One caveat I would have is that the analyses presented assume that the heat is evenly distributed into the entire air stream.

As posed in the OP, if the 1-kW source is small compared to the dimensions of the duct opening, the local air temperature might be considerably higher.

TTFN

FAQ731-376
 
Another more intuitive view is to consider that 2500 CFM is equivalent to exchanging the air in a 17 ft x 17 ft x 8 ft room EVERY minute. Now add 5 PCs into the room. What little heat they're generating is trivially removed by the air flow