Deadblow
Structural
- Jul 13, 2015
- 141
Hello All,
I am working on the design of a 6'-0" tall shipping dock wall. It will be 12" cmu grouted solid. I referred to NCMA TEK 14-7B and was able to analyze the wall utilizing the rectangular beam analysis. This analysis proved that the wall needs #5 bar at 40" o/c for flexure. My question is in regards to shear and the tables provided in NCMA TEK 14-19A (attached). The allowable shear stress, Fv, is equal to sq. root of f'm of 1500psi, 50psi maximum. So Fv for my wall = 38.7psi. If you look at the eighth bullet point on the first page, it states "walls are grouted only at cores containing reinforcement". So when I look at the table for 12" thick cmu with d=5.813, I see that almost all of options have a resisting shear capacity of 2,701 lb/ft. How do they arrive at this number? Why is it the same for walls grouted at 8" o/c through 72" o/c?
I know that 2701/(12x5.813)= 38.7psi. So it appears to me that these tables are accounting for shear strength from cores that are not filled with grout and are just air. Thoughts?
Lastly, why does the shear capacity change for bars spaced more than 72" apart?
Thanks
I am working on the design of a 6'-0" tall shipping dock wall. It will be 12" cmu grouted solid. I referred to NCMA TEK 14-7B and was able to analyze the wall utilizing the rectangular beam analysis. This analysis proved that the wall needs #5 bar at 40" o/c for flexure. My question is in regards to shear and the tables provided in NCMA TEK 14-19A (attached). The allowable shear stress, Fv, is equal to sq. root of f'm of 1500psi, 50psi maximum. So Fv for my wall = 38.7psi. If you look at the eighth bullet point on the first page, it states "walls are grouted only at cores containing reinforcement". So when I look at the table for 12" thick cmu with d=5.813, I see that almost all of options have a resisting shear capacity of 2,701 lb/ft. How do they arrive at this number? Why is it the same for walls grouted at 8" o/c through 72" o/c?
I know that 2701/(12x5.813)= 38.7psi. So it appears to me that these tables are accounting for shear strength from cores that are not filled with grout and are just air. Thoughts?
Lastly, why does the shear capacity change for bars spaced more than 72" apart?
Thanks