ekuegler
Electrical
- Jan 2, 2012
- 38
Hi all,
Can you explain the effects of a large imbalance between phases R-Y, R-B = 0.38 milli ohm Y-B = 4 ohm when a generator is ductored, IR/PI good.
Star bar disconnected, IR between phases good. Line to line ductor all 3 phases identical. Only when star bar connected is there an issue when ductoring.
Unit didn't trip on any protection type, severe weather to cut a long story short caused Shutdown and consequently seawater/lube oil to enter alternator enclosure/ submerge stator 1/4 way up, now drained down awaiting chemical clean.
Can this unit be ran once cleaned with the large imbalance as above? Could interturn failire be a cause?Surely the diff protection would have operated in this instance....?
Any thoughts on alternate tests to carryout to pin point route cause. Strange situation given it ran with no known issues/alarms prior to unit shutdown due the plant ESD.
Can you explain the effects of a large imbalance between phases R-Y, R-B = 0.38 milli ohm Y-B = 4 ohm when a generator is ductored, IR/PI good.
Star bar disconnected, IR between phases good. Line to line ductor all 3 phases identical. Only when star bar connected is there an issue when ductoring.
Unit didn't trip on any protection type, severe weather to cut a long story short caused Shutdown and consequently seawater/lube oil to enter alternator enclosure/ submerge stator 1/4 way up, now drained down awaiting chemical clean.
Can this unit be ran once cleaned with the large imbalance as above? Could interturn failire be a cause?Surely the diff protection would have operated in this instance....?
Any thoughts on alternate tests to carryout to pin point route cause. Strange situation given it ran with no known issues/alarms prior to unit shutdown due the plant ESD.