While performing maintenance on a UPS we run our gens and do a wrap around feed to a distribution board. The power going through the bypass breaker and the power for the wrap around is coming from the same Emergency buss. When 1 of the 2 paralleled feeds is energized, current readings are approximately 40 amps per phase measured with a clamp on meter and by the Power logic system. When both feeds are energized; because they are paralleled we would expect the load to be approximately 20 amps per phase, per feeder. What we see with a clamp on meter is 50 to 70 amps per phase on 1 feeder and 60 to 90 amps per phase on the other feeder; but Power Logic still reports 40 amps per phase. This is not a problem I am just trying to figure out what is happening to better understand this anomaly. Thanks