I am doing a residential project where there is an existing 2 story house and they are adding a new front balcony.
The existing floor joists cantilever 3.5ft and support the wall (roof) above.

Since this isn't the best condition I am adding a steel beam under the wall above so that I can cantilever new deck joists out for the new balcony. I am extending the new deck joists 7ft back into the existing floor framing and sistering them to the existing floor joists.

I am having problems correctly analyzing the reactions to the new steel beam.
Would the rxn at the new stl beam just be the entire fj/dj span with 3 simply supported rxns?

Partial framing plan attached

Thanks
 
 https://files.engineering.com/getfile.aspx?folder=02ca557e-b23e-4350-9163-bbb2a9d205e1&file=FJDJ.pdf
Replies continue below

Recommended for you

beav-eng, I have already sketched it but I am not 100% sure about the reactions.
I initially assumed that the reactions would be the fbd of the entire new & existing joist section with 3 rxn's.

The beam is 18'-6" it supports roof, floor and balcony. 40psf LL & 60psf LL for balcony. A wood bm works but it is 16" deep. Thats why I'm using steel.

Thanks Lex, see attached .jpg. Red is the new framing.
jsts_n5lpk5.jpg
 